OK to swap B MCB for Type C or does my C load have to go on it's own breaker? | on ElectriciansForums

Discuss OK to swap B MCB for Type C or does my C load have to go on it's own breaker? in the UK Electrical Forum area at ElectriciansForums.net

Msitekkie

-
Arms
Joined
Apr 24, 2017
Messages
111
Reaction score
18
Location
Essex
I have a customer who want's me to fit a 3Kw Patio heaterto a garage. - I believe this requires a Type C breaker. There is limited space in the board, so wanted to get peoples views on whether it's OK to swap an existing B type (used for sockets) for the C type, or whether the C type load needs to be on it's own breaker. I guess really the question is whether it's OK for the garage sockets to be on the C breaker.
 
"The unit should be protected by a suitably rated isolator and fuse or type C MCB. An inrush current (initial current through the lamp) can be expected at switch on. This current can be as high as 12 times the normal operating current, lasting less than 20 milliseconds. This effect can also vary depending on temperature. In extreme cases, a type D breaker may be required."
NB do not be thrown off by the use of the word "lamp" here.

But we digress. Even if type C were not required, for future reference I would still like to understand the scenario/implications of using sockets (with normal loads) in conjunction with a C type breaker.
If its a heater then there’s no need for a type C.
 
"The unit should be protected by a suitably rated isolator and fuse or type C MCB. An inrush current (initial current through the lamp) can be expected at switch on. This current can be as high as 12 times the normal operating current, lasting less than 20 milliseconds. This effect can also vary depending on temperature. In extreme cases, a type D breaker may be required."
NB do not be thrown off by the use of the word "lamp" here.
OK so some "halogen" style heater?
But we digress. Even if type C were not required, for future reference I would still like to understand the scenario/implications of using sockets (with normal loads) in conjunction with a C type breaker.
The real difference between B/C/D is the "instant" trip point which results in quick disconnection for fault protection, rather than the thermal overload part. The regulations require automatic disconnection in under 0.4s for a nominal 230V TN supplied system so for MCB clearing of faults you need to reach that point.

So as you go B -> C -> D your maximum end of circuit Zs halves each time.

The UK style of 13A sockets don't care, they have their own fuse for fault/overload disconnection, but your circuit design for the socket fixed wiring becomes harder to meet for long runs. Yes, you can also meet disconnection on the RCD side of things quite legitimately (as you almost always need to on a TT supply) but I personally would aim to meet it on the MCB side if practical.
 
Just to add, that patio heater's inrush is specified at 157A (12 * 13.04A), which is pretty punishing for any switches. But it is implying you would need a 32A C-curve supply or 16A D-curve.

It also puts it in the middle of the standard 13A fuse's trip curve, so I suspect this might need a dedicated 16A supply with D-curve MCB and a 20A isolation switch (i.e. not a socket of FCU).

[ElectriciansForums.net] OK to swap B MCB for Type C or does my C load have to go on it's own breaker?
 
Last edited:
OK so some "halogen" style heater?

The real difference between B/C/D is the "instant" trip point which results in quick disconnection for fault protection, rather than the thermal overload part. The regulations require automatic disconnection in under 0.4s for a nominal 230V TN supplied system so for MCB clearing of faults you need to reach that point.

So as you go B -> C -> D your maximum end of circuit Zs halves each time.

The UK style of 13A sockets don't care, they have their own fuse for fault/overload disconnection, but your circuit design for the socket fixed wiring becomes harder to meet for long runs. Yes, you can also meet disconnection on the RCD side of things quite legitimately (as you almost always need to on a TT supply) but I personally would aim to meet it on the MCB side if practical.
That's really helpful, thanks.
 

Reply to OK to swap B MCB for Type C or does my C load have to go on it's own breaker? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top