old thermostat can I do away with terminals 2 and earth and install a standard common and normally open thermostat

Old thermostat
2 neutral
3 normally open
1 common

9EE08073-B495-48B7-821A-E7E75E72E9E0.jpeg


C5B103E7-504F-4336-B5A0-BF400BAA872B.jpeg
 
If the new thermostat does not require a neutral then no, you don't need to connect a neutral to it. However you do need to make that conductor safe rather than just sticking tape over it!
You can't just do away with the earth as the regulations require that it be present at every pount of termination, the obvious issue here is that cable doesn't have an earth in it, so you need to assess whether a class 2 thermostat will maintain the required level of safety or whether something else needs to be done.
 
Top picture the old stat and bottom the new one?

Do you have a neutral taped up?

It's used to hone the switching temperature hysteresis, so it's not needed but better being there. Although if that bottom pic is the new on, there is no connection for either an earth (CPC) or neutral.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
Business Name
Platinum electrical

Thread Information

Title
Old and new Thermostat wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
chris day,
Last reply from
nunthe wiser,
Replies
3
Views
1,452

Advert

TrueNAS JBOD Storage Server

Back
Top