I understand that this may be an impossible one to answer, but I have been surprised on many occasions with what info is out there if you only ask. So here goes.

I am trying to locate historical cable data sheets for paper lead cables that were probably installed in the 1960s

I think that the manufacture was probably BICC who are no longer in existence. I have done a google search and found a company in Cairo who carry the BICC logo. I have emailed them but as yet had no reply.

The cables are imperial 2 core 19/0.64 and 19/1.53 lead sheathed,

The specific info I am looking for is the ohmic values of the conductors and lead sheath. Similar to the Table 11 in the onsite guide R1 + R2 values.

Thanks

Steve
 
As I had to swing by the stores yesterday, I picked up some relevant info. There wasn't time to search for the books nearest to the date of your cable, as some of it is still boxed up from the move, so what I ended up with is all older than your assumed 1960s cable.

The first thing I noticed is the lack of 19/.103 conductors in the tables. There's 19/.101 hard-drawn copper but not annealed, so not relevant IMO, the largest 19-strand annealed conductor being 19/.083 at 0.1 sq. ins. So I think it is worth just double-checking your reference for the larger cable; i.e. where did the 95mm² and 19/something figures come from? Could it be a 0.15 sq. ins. cable of different stranding such as 37/.072?

Also, do you have the voltage rating or BS for the cables?

Looking only at the smaller cable for now:

BICC 'Cables & Tables' 1953 ed.
Quoting BS7 for 19/.064 annealed copper conductor at 20°C:
Standard resistance per 1000 yds. 0.4074Ω
Maximum for tinned conductors per 1000 yds. 0.4195Ω
Weight per 1000 yds: 720.3 lbs

Table 8, quoting IEE 12th ed, for one or two 2-core PILC 0.15 sq. ins. cable at 32°C ambient:
CCC: 128A DC or 1-phase AC
Voltage drop: one volt per 24 feet DC or 1-phase AC

No info on the lead sheath.

The first reference I have found to the lead thickness for a 660V cable is actually from before the BICC merger:
BIC handbook 4th. ed. of 1927.
For 660V twin plain class A PILC with either circular or segmental 0.06 sq. ins. conductor:
Lead thickness 0.080 ins
Diameter overall: 0.85 ins.
Weight per 1000 yds. 43.75 cwt.


For comparison, from a different manufacturer nearer in date to your cable and probably to the correct BS:
Enfield Standard Power Cable Handbook ES101 of August 1962, paper insulated cables to to BS480 : 1954
Table 2.2, twin-core belted 1100V cable with segmental 19/.064 conductors, type PLY (bare sheath)
Minimum thickness of sheath 0.05 ins.
Nominal diameter overall: 0.78 ins.
Approx. weight per 1000 yds: 30cwt.

Next tea break I will bash the numbers into the calculator and see what we get for the lead resistances.
16126114269455389720090770870102.jpg
1612611462946217565130229176999.jpg
16126115332449194621712821357991.jpg
 
Last edited:
Let's try to validate the lead CSA for the older BIC 19/.064 by calculating it both from the stated dimensions and from the linear weights.

Lead O/D = 0.85 ins. = 21.59mm
Lead I/D = 0.85 - (2 * 0.08) = 0.69 ins. = 17.53mm
Lead CSA from dims = ((21.59 / 2)² - (17.53 / 2)²) * Π = 125mm²

Weight of twin cable = 43.75cwt / 1000 yds. = 2.431kg/m
Weight of 19/.064 copper = 720.3 lbs / 1000 yds. = 0.3573kg/m
Weight of lead (ignoring paper) = 2.431 - (2 * 0.3573) = 1.7164kg/m
Lead density (ignoring alloying elements) = 11.34g/cm³
Lead volume per metre = 1716.4 / 11.34 = 151.4cm³
Lead CSA from weight = 151mm²

Lead resistivity 2.2E-7 Ωm @ 20°C ignoring alloying.
Resistance of 125mm² lead = 2.2E-7 / 125E-6 = 1.76mΩ/m
Resistance of 151mm² lead = 2.2E-7 / 151E-6 = 1.46mΩ/m
Resistance of 19/.064 TC = 0.4195Ω / 1000 yds. = 0.459mΩ/m

I'll do the later Enfield cable in the morning unless someone wants to save me the effort.
 
Last edited:
Resistance of 125mm² lead = 2.2E-7 / 125E-6 = 1.76mΩ/m
Resistance of 151mm² lead = 2.2E-7 / 151E-6 = 1.46mΩ/m
Resistance of 19/.064 TC = 0.4195Ω / 1000 yds. = 0.459mΩ/m
Comparing that to 2-core 35mm SWA which looks closes today I see R1 as 0.524 mOhm/m and the armour R2 as 2.6mOhm/m, so the lead sheathed cable is better!

For a given definition based on Zs (or more specifically R2/R1 as about 5 for SWA and about 3.8 for old stuff) and using the Prysmian data sheet for BS5467 cable
 
The Enfield cable has a thinner sheath so might be closer to SWA. Obviously some PILC has wire armour in parallel, some has tape which is less beneficial as a CPC.

Hopefully the OP will be able to confirm the larger cable data and if I go to the warehouse tomorrow I will have a look for 1960s data books.

In the meantime, while we're doing electrical-industry-promotional-items-on-radios here's a pocket electrical slide-rule from Hackbridge and Hewittic (the transformer and rectifier people)
16126980296973003746131877260250.jpg
 
Yes, one of the MMs that won't be working any time soon due to disintegrated Mazak castings in the tuning gang.
 
Let's try to validate the lead CSA for the older BIC 19/.064 by calculating it both from the stated dimensions and from the linear weights.

Lead O/D = 0.85 ins. = 21.59mm
Lead I/D = 0.85 - (2 * 0.08) = 0.69 ins. = 17.53mm
Lead CSA from dims = ((21.59 / 2)² - (17.53 / 2)²) * Π = 125mm²

Weight of twin cable = 43.75cwt / 1000 yds. = 2.431kg/m
Weight of 19/.064 copper = 720.3 lbs / 1000 yds. = 0.3573kg/m
Weight of lead (ignoring paper) = 2.431 - (2 * 0.3573) = 1.7164kg/m
Lead density (ignoring alloying elements) = 11.34g/cm³
Lead volume per metre = 1716.4 / 11.34 = 151.4cm³
Lead CSA from weight = 151mm²

Lead resistivity 2.2E-7 Ωm @ 20°C ignoring alloying.
Resistance of 125mm² lead = 2.2E-7 / 125E-6 = 1.76mΩ/m
Resistance of 151mm² lead = 2.2E-7 / 151E-6 = 1.46mΩ/m
Resistance of 19/.064 TC = 0.4195Ω / 1000 yds. = 0.459mΩ/m

I'll do the later Enfield cable in the morning unless someone wants to save me the effort.
Lucian

This brilliant. I cant believe you have gone to this amount of effort to help.

Perhaps the best way would take an average of the 125mm² and the 151mm². That's probably a reasonable assumption.

You did mention the lack of 19/.103, this should be 19/153.

if you could assist with the larger cable that would be much appreciated.

Steve
 
Feel free to mash the winner button if you like the service!

I didn't get round to the later Enfield 19/.064 cable yet, that is more likely to be of similar construction to your 1960s cable as they were probably both made to the later British Standard. The lead is significantly thinner so we should calculate that before making a final call on the sheath resistance.

Re the larger cable, I can't make sense of the '19/153' or '19/1.53' as given earlier.
  • 19/1.53 is a valid metric cable stranding for 35mm²
  • Trying to read it as an imperial size '19/.153' would make it 225mm²
  • My reference to 19/.103 was a top-of head attempt to match it to your comment that it was 95mm² equivalent. 19/.103 did exist as a stranding and is just over 95mm², but does not seem to have been used as a core of PILC.
  • 95mm² equivalent imperial size as a PILC core invariably seems to have been 37/.072
So we really need to clarify that number and gather any other possible information before we can make headway with the larger cable.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Old cable data sheets.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
Gnasher,
Last reply from
Lucien Nunes,
Replies
28
Views
5,591

Advert

Back
Top