old installation, only 1 set of cables. | on ElectriciansForums

Discuss old installation, only 1 set of cables. in the Talk Electrician area at ElectriciansForums.net

R

rabu

Hi. can anyone help me, been doing few bits at home, swapping light switches and replacing some old sockets.. anyway after noticing that couple of sockets only had 1 cable in, so was thinking that they were spurs. That got me into tracing them, seeing how the house has been wired, so been looking in sockets to see what cables there is. Not got round to lifing floorboards. However most of the sockets iv opened (most in the house) only have 1 cable, some i know are spurs but some of the origionals from building only have 1 set inside also some are in stranded copper looks quite thick possibly 7 strands others in 2.5mm. Is there a way of wiring circuits that doesnt involve linking sockets directly from last socket? e.g: the use of junction boxes under floors? so can anyone shed any light on why i only have 1 set of cables in sockets? also lights have 2 or 3 (cant remmeber of hand) single red cables, all stranded copper with i think 2 black cables in roses with 1 red (cant be certain withought looking) Thank for any help.
 
The wiring you have discribed sounds like 40yrs+ old approx. Singles on lighting no earth. I would recommend that you contact a local electrician to carry out a periodic inspection report for you. This will determine the condition of the installation and will detail any recommendations. I would not carry out anymore work untill you have contacted an electrician. If there are no earths on the lighting and you have not got any RCD protection it would be unsafe to have any metal/chrome switches or metal light fittings installed. Be safe and get it tested.
 
In older installations you may well find that the ring final only serves junction boxes and then a leg taken from each jb to the socket outlet.
 
second that. sounds like JBs under floor. the 7 stranded cable will be 7/029 used up to the 70's. is it pvc though or rubber? if it's rubber, then it's a rewire.
 
Agree with others on the JB setup, but Ive also seen a single ring either up or down with a socket spurred of each to feed either up or down.
 
Agree with others on the JB setup, but Ive also seen a single ring either up or down with a socket spurred of each to feed either up or down.

but then he'd have 3 cables in a socket. he's only got one in each
 
thanks everyone. what the last 2 replies described are simalar as what iv been finding,or thinking that a main cable runs under floors with a cable of from JB up to sockets. regards to safty, the wiring is (most of ot) from 1965 when house was built. more new things added over years are 2.5mm solid core. all cable in house is PVC insulated just some is stranded and other is solid core. dont think theres earths in lights. thers been no issues with fuses blowing only cooker fuse (cooker element failed) or any other wiring issues. Might get it checked but wiring seems ok, no known issues. my main thing was the way sockets have been wired with 1 set of cables. Would this type of wiring be a ring final circuit or radial? Thanks again to everyone.
 
just a quick update, this is out main consumer unit/ fuse box. meter and DNO fuse replaced about 2008/09 Thanks again to everyone.
[ElectriciansForums.net] old installation, only 1 set of cables.
 
only way to see if it's a ring is to look at the fuse. if 30A it should be a ring. then there will be 2 reds in the top of the fuse. with the main switch off, disconnect these reds and their associated neutrals and cpc's and meter red/red/, bk/bk, cpc/cpc. if you get continuity, then it's a ring.
 
You might get it checked but it seems ok?

The wiring is in excess of 46 years old, installations have an average safe working life of between 20 and 40 years!

What were your insulation resistance values? I'm curious how you've arrived at the "seems ok" assessment.
 
Are you replacing the switches with metal or plastic fittings? Just because the fuses havent blown does not mean that the installation is safe. It is recommended that an installation is tested every 10yrs. If there is a fault on a metal fitting it could become live and with no earths it may not be found untill it is touched.
 
I'll bet the Bill Switchgear fusebox has asbestos flashguards too!

Is this post a wind-up?
 
That old grey Bill CU will have asbestos flash guards and really should be replaced.

Also, the main switches also have a habit of snapping off when you go to isolate the installation, and it usually snaps in the closed position.
 
well PVC insulation, not rubber. also, if things were faulty (say in terminal connections) this would blow fuse? all fitting old and new are plastic. "average safe working life of between 20 and 40 years!" so every 20 years people need rewires? "seems ok" well apart from insulation still intack, better than being dust and dropping off. only half the wiring is origional, as it was a bungalow so in mid - late 70s dormers were build meaning upstairs isnt as old and is done in 2.5mm T&E. also a mate (semi retired spark) whos not seen instalation yet has said is should be ok, proving its PVC cable and nothing buring or getting hot or fuses blowing, indicating faults. but thanks again to the people who shed the light on the wiring issues.
 
It a bit worrying that theres been additions i.e. extra sockets and you are not sure if it is a radial or a ring main. Has the fuses been checked to make sure they are the correct size, or is there a nail instead. I have found fuses with 2.5mm copper rather than the correct sized fuse wire. Certainly stops the nuisance tripping ( fuse blowing ).
 
Last edited by a moderator:

Reply to old installation, only 1 set of cables. in the Talk Electrician area at ElectriciansForums.net

Similar Threads

I think I've found the answers to my questions... I can just do a straight forward wiring i.e. connect the 3 wires from the armoured cable to...
Replies
7
Views
829
Sounds more positive.
Replies
8
Views
475
Often in old wiring, live to the downstairs switch, then in twin (or twin & earth) the two switched lives to the upstairs switch, and a single...
Replies
4
Views
251
It might be ok
Replies
6
Views
470
Definitely looks like the cpc (earth) has been sleeved and used as a neutral conductor, this is not permitted. You are going to need an...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks