guys im replacing an electric shower like for like, the old shower was 9.5 kw, but was only on a 32 a mem type 1 321 qeb mcb, i told cliant it should be protected by a 40 amp breaker, trouble is the board is oldish and i dont know what breaker to fit,,,, also no rcd protection on boaed, are there any mem rcbo that will fit that board,tanx
 
230v EU!! as said above... however my property enjoys a nice helping of 244V !! i would measure the supply to see what you actually get! some times you can be suprised..! i once saw a reading of 252v that dropped off in the day to 241....!! hmm interesting
 
ya if it's up over 240v you can add a kilowatt to the load- best check supply voltage as it could affect mcb/cabling

as you said they're marked on the box 8.5/9.5 for 230/240 that's why i assumed you were mostly still on 240v in the uk


DSO here is allowed 10% tolerance (23volt either side of 230v) -but that would be extreme
 
Last edited by a moderator:
I've had a 10.5kw shower wired in 10mm, for 10 years...on a 32a rcd breaker...never tripped yet..its only on a 32a cos at the time i had one spare...never got round to changing to 40a, no need to now
 
hmm 10.5kw is a big shower-you sure it's that big :confused:

it should trip over time anyhow -according to the characteristic curve of the mcb

i've been miscalculating slightly anyhow-9.5 at 240v =<40amp and 10.5 at 240v =<44amp

i was a bit confused as the uk nominal voltage is now 230 but appararently it can be 240(and also above or below with tolerances)
 
Last edited by a moderator:
guys im replacing an electric shower like for like, the old shower was 9.5 kw, but was only on a 32 a mem type 1 321 qeb mcb, i told cliant it should be protected by a 40 amp breaker, trouble is the board is oldish and i dont know what breaker to fit,,,, also no rcd protection on boaed, are there any mem rcbo that will fit that board,tanx



Have you considered checking if there is any significant earth leakage and if not, protecting the whole board with a separate rcd in the tails.
 
you might just get away with the 6sq on that-it's borderline around the 9kw


down to the install method and length of run really
10sq is usually a safer bet anyway
 
Last edited by a moderator:

Reply to old mem consumer unit, help plezzzzzz in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
137
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
928
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
873
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top