Got an EICR next week, been a doctors surgery for couple yrs, but electrics outdate building by 20+ yrs.

2 old rewirable fuse DB's with 20 circuits supplying whole place, my thoughts are seems as use of building has changed then some remedials are required such as no rcd sockets for cleaners etc.

But if i do that where does it stop? obviously cables buried in walls but would be over the top rcd protecting all circuits.

Was just wondering what some of you would do in this case?
 
Has to be the best judgement of the tester to outline any defects from current regs bering in mind if it complied at the time or at all and the benefits of upgrading with regards to modern protection to comply to electricity at work regs and current requirements.
Have offen found frightening a client tends to have an adverse effect on safety and what they have done so best to explain regulations in conjusction with your findings.
 
Thats the trouble, obviously complied when installed, but now the use of building has changed and as i see it so should the installation to protect all staff/ visitors and cleaners.

I suppose being under supervision as there is management for the building rcd protection for circuits buried etc can be left out but mainly cleaners/ general sockets should be protected.
 
When the building was converted to a Dr's surgery, was it / is it an NHS "establishment"?
If so were MEGiAN or any HTM's considered, as these would over rule BS7671 and would have at the time.
They are also retrospective IIRC, so, if the surgery does not comply now then it is doubtful it complied then, so it should not pass as 7671 also includes a reference to complying with other required standards.
There are more to medical locations than the current section 710.
 
The buildings purpose may have changed but has the risk to the users of the electrical system increased ?
You have to be the judge of this as the inspector and carry out a risk assessment as if you were a member of staff.
Personnally , and without looking at the job , i'd say no.
In which case i'd code the lack of rcds as code3 , similar to what you'd do if it was a domestic and the regs are not retrospective whether domestic , commmercial or industrial.
Health centres and clinics were perfectly safe locations before rcd's were invented.
 
Not NHS its a private clinic.

Do they undertake "contract" work for the NHS, at all, IF they do then HTM's WILL apply.
Even if they don't MEiGAN will apply.
AFAIK both of these are retrospective, and should have been applied at the change of use.
I will check this out, and also get it independently checked.
However, it is not quite that simple as to the practice being private thus x, y & z not applying.
Whilst 7671 is not retrospective, certain other statutory and other regulations are.
 
Health centres and clinics were perfectly safe locations before rcd's were invented.

biff55,
Yes they were, but were there such a plethora of electrical appliances used as applied parts at that time, I suspect not!
Remember, that there may well be invasive surgery being undertaken at this location, which may well involve electrical appliances in ways which were not even contemplated back in the day before RCD's! ;)
 
You can buy the HTM's but they are eye watering in comparison to 7671!
MEiGAN or at least its guidance is downloadable if you search for it.
If they are a legitimate NHS practice they may have access to the HTM's.
 
biff55,
Yes they were, but were there such a plethora of electrical appliances used as applied parts at that time, I suspect not!
Remember, that there may well be invasive surgery being undertaken at this location, which may well involve electrical appliances in ways which were not even contemplated back in the day before RCD's! ;)

Good point but.....
Appliances would be covered under pat testing not BS7671.
And if theres surgery being done ( unlikely in a converted house unless its Dr. frankenstien ) then you deffinatley dont want to go banging in rcd's that could trip at crucial moments.
 
Yes biff appliances would be the area of "PAT" not BS7671.
However, medical appliances would not be "PAT" either, they have their own rules especially if they are patient treatment devices.
Your average PAT machine would be woefully inadequate to test to the requirements of some of this kit.
The reason I am a little, and only a little clued up on this is that I do work for my local health trust in benign environments, however there are applied parts, and we are discussing my taking on some medical equipment testing for them, and this will necessitate another piece of test equipment, which makes the price of a Seaward Supernova look like small change!

It is the electrical system that you connect them to that I am suggesting could be the weak point.
There are also many GP surgeries that now undertake minor surgical procedures, this is one of the reasons that 710 has come in.
However, this is minor in comparison to other requirements.
Remember also 7671 requires compliance with manufacturers instructions.
For med stuff these will almost certainly require compliance of the fixed install to things that are not even in 710!
 

Reply to old rewirable Db's in doctors.. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
Absence of correct labelling is a C3, reversed polarity is a C1 (BPG-4). You choose.
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top