Andy C

-
Joined
Nov 26, 2016
Messages
89
Reaction score
23
Location
Wirral
I have been doing some work for a hedgehog charity so funds have been tight.
I have remedied a number of non conformity items as they want an EICR for the landlord.

I am happy with the general condition of the circuits and readings are all within range. A number of C3s have been given, with one being lack of cable support in ceiling areas.

The shop has two Wylex boards one metalclad and one plastic. Neither has a lid for where the original rewirable fuses were as these have been replaced with MCBs of various types. I intend to replace the fuse carriers that have open pin connections to closed ones. Doing this, will it be sufficient to pass as there will still be no lid/cover on either board.

The boards are in a cupboard that is secure and only authorised staff have access to.

I have considered sourcing new lids but they would still need the cover cutting out so the MCBs would fit.

The final option is replacement DBs but I want to avoid the cost if I can.

Thanks for any replies.
 
Can you touch any live parts with these fuse cover missing, I used to think the same but the gap is very small around the edge it has to be IP2x and I don't think you can get your finger in to touch the live bus bar. Yes I agree you could touch the live pins when removing fuses , but that is the case with a lot of old boards that are still in service in factory's throughout the land , May be a label saying " warning turn off main switch before removing fuses" may be the answer
 
Can you touch any live parts with these fuse cover missing, I used to think the same but the gap is very small around the edge it has to be IP2x and I don't think you can get your finger in to touch the live bus bar. Yes I agree you could touch the live pins when removing fuses , but that is the case with a lot of old boards that are still in service in factory's throughout the land , May be a label saying " warning turn off main switch before removing fuses" may be the answer
All you need to do is tilt a fuse and live parts on the fuse itself are finger accessible, there is a warning on these boards to switch off before handling fuses, not good enough to comply with current requirements IMO. Many of these boards are in understairs cupboards with covers missing easily reached by curious kids. It surprises me there are not more electrocutions.
 
Yes times have changed and we are now more aware of dangers these days so it may be a good idea to advise people of the dangers and what can be done to improve things .
In a domestic environment yes it would be a good idea to recomend replacing such a CU to make it safer, especially has you say if children can easily access it , but in a commercial environment it would be easier to police for example method statements, stating employees are not permited to touch any electrical equipment , I have been to places that don't let employee's change light bulbs or go up steps ladders.Now I know people may ignore these rules but you can't protect people from their own stupidity
 

Reply to Old Wylex DBs no lids. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ah my mistake - apologies. I have something more or less like this wylex unit and the flappy plastic cover has got a broken pin so won't stay one...
Replies
4
Views
276
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
190

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top