Sorry for the late reply, took advantage of some clear weather today to take the ankle biters out...till it ruddy rained anyway!
Anyway, I checked our shower thoroughly, and can confirm the following are installed;
2 x Thermocouples
1 x manual reset bimetal thermal sensor
1 x Pressure transducer
1 x flow sensor
1 x overload sensor (magnetic)
Based on this I have to concur will all comments by Gavin and initially by DW. With this level of protection in the unit then realistically an RCD protecting the Unit would be sufficient for compliance with the Regs at the basic fault protection level, although personally I would still, if I installed a shower, use a correctly rated RCBO to cover both bases.
Many thanks Guys, It's always good to learn and I love things that make me investigate and perhaps, as in this case, change how I think about something...Nice one.