Been reading various threads with regards to having an mcb that exceeds the cable rating thus only providing short circuit protection, what surprises me is the negative responses that are posted if it is ever suggested.
Now lets try put a translation on the regulation specifically 433-3-1 (ii)
A device for protection against overload need not be provided:
(ii)- for a conductor which because of the characteristics of the load or the supply , is not likely to carry overload current, provided the conductor is protected against fault current in accordance with the requirements of section 434.
This particular regulation is can be applied when the load is fixed or by the nature of the load and its control system an overload is unlikely to occur as in a motor circuit where an overload device will be monitoring the motor in its control system. It can also be used for say a shower circuit or water heater etc however having said this it is however usual to provide overload protection unless it is impracticable to do so.
What im getting at here is you really shouldn't be applying this regulation to your domestic shower if your are wiring it but it can sometimes be utilised if say you fit a larger shower within the ccc of the cable but by the nature of mcb ratings you find your mcb slightly over the ccc rating of the cable.... but all other calcs must comply as normal. I want to stress it shouldn't be applied routinely in domestic install but is permitted but as a rule don't use it in your designs. Where this regulation comes into more common use as i do often have to imply it is supplying motors and machinery and by the nature of inrush a mcb (even d rated) would nuisance trip because it is lower than the ccc of the cable it protects... fitting a higher rated mcb can omit nuisance tripping and overload isn't an issue as the motor has its own overload protection.
So please can we stop throwing this regulation at members when discussing showers etc as this becomes misleading to the OP who might not be as clued up on the nature of this regulation.... yes its allowed but it shouldn't be practiced in the domestic realm.
Now lets try put a translation on the regulation specifically 433-3-1 (ii)
A device for protection against overload need not be provided:
(ii)- for a conductor which because of the characteristics of the load or the supply , is not likely to carry overload current, provided the conductor is protected against fault current in accordance with the requirements of section 434.
This particular regulation is can be applied when the load is fixed or by the nature of the load and its control system an overload is unlikely to occur as in a motor circuit where an overload device will be monitoring the motor in its control system. It can also be used for say a shower circuit or water heater etc however having said this it is however usual to provide overload protection unless it is impracticable to do so.
What im getting at here is you really shouldn't be applying this regulation to your domestic shower if your are wiring it but it can sometimes be utilised if say you fit a larger shower within the ccc of the cable but by the nature of mcb ratings you find your mcb slightly over the ccc rating of the cable.... but all other calcs must comply as normal. I want to stress it shouldn't be applied routinely in domestic install but is permitted but as a rule don't use it in your designs. Where this regulation comes into more common use as i do often have to imply it is supplying motors and machinery and by the nature of inrush a mcb (even d rated) would nuisance trip because it is lower than the ccc of the cable it protects... fitting a higher rated mcb can omit nuisance tripping and overload isn't an issue as the motor has its own overload protection.
So please can we stop throwing this regulation at members when discussing showers etc as this becomes misleading to the OP who might not be as clued up on the nature of this regulation.... yes its allowed but it shouldn't be practiced in the domestic realm.