I would just like to run this one past people.
Customer has three sockets in a kitchen wired as a ring.
The two legs of 2.5mm T and E from this ring come through the wall into a cupboard.
A junction box has been fitted and a single 2.5 T and E then goes back to the DB fused at 32A (don't ask me why FK knows).
Obviously I need to replace the cable from this junction box in the cupboard to the DB.
I was thinking of using 4mm cable as it is quite a tricky route and one cable surface clipped would look neater than two.
So my question is would it be OK to run 4mm from the DB to this junction box where the 4mm cable will then be turned into two legs of a ring each of 2.5 T and E.
I am 99% positive it will be OK but just in case am I wrong?
Thanks.