Hi. I'm hoping someone can help with a question about adding a socket as a spur onto a ring mains circuit (rcd protected at CU).
Its a 2 gang socket so max load could be 26A. The 2.5 TE cable is rated for 27A but this reduces to maybe 20A if its in buried in a wall in conduit (as it will be). Its not a long run (500 mm) and its unlikely anyone is going to plug two electric heaters into it, but would is this something to worry about? Would it be OK/advisable to label as, perhaps, max 13 A total load? many thanks.
 
Hi. I'm hoping someone can help with a question about adding a socket as a spur onto a ring mains circuit (rcd protected at CU).
Its a 2 gang socket so max load could be 26A. The 2.5 TE cable is rated for 27A but this reduces to maybe 20A if its in buried in a wall in conduit (as it will be). Its not a long run (500 mm) and its unlikely anyone is going to plug two electric heaters into it, but would is this something to worry about? Would it be OK/advisable to label as, perhaps, max 13 A total load? many thanks.
You can legitimately take a spur as you suggest, as long as there isn't already a spur at that point!
The derating is to ensure sustained loads don't damage the cable, (and allows for two such cables in the conduit).
As you point out, it's unlikely anyone would run a 6kW load continuously from that socket (if a heater it would turn itself off after a while, unless you live in a barn!) so I think many would say it's not an issue to do as you propose, even without a label.

To comply with the derating factor, you could use 4.0mm2 T&E, though getting 2 x 2.5mm + 1 x 4.0mm into the ring socket may prove fiddly! One of these would work: https://www.screwfix.com/p/mk-logic-plus-rapid-fix-13a-2-gang-dp-switched-socket-white/814ph
An electrical wholesaler would sell you 1m of cable!
 
You can legitimately take a spur as you suggest, as long as there isn't already a spur at that point!
The derating is to ensure sustained loads don't damage the cable, (and allows for two such cables in the conduit).
As you point out, it's unlikely anyone would run a 6kW load continuously from that socket (if a heater it would turn itself off after a while, unless you live in a barn!) so I think many would say it's not an issue to do as you propose, even without a label.

To comply with the derating factor, you could use 4.0mm2 T&E, though getting 2 x 2.5mm + 1 x 4.0mm into the ring socket may prove fiddly! One of these would work: https://www.screwfix.com/p/mk-logic-plus-rapid-fix-13a-2-gang-dp-switched-socket-white/814ph
An electrical wholesaler would sell you 1m of cable!
Many thanks. Very clear!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
Business Name
University of Southampto

Thread Information

Title
Socket on spur with cable in conduit
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
GrahamP,
Last reply from
GrahamP,
Replies
2
Views
334

Advert

TrueNAS JBOD Storage Server

Back
Top