One string or two? | on ElectriciansForums

Discuss One string or two? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Colin33

-
Arms
Joined
Jul 27, 2010
Messages
215
Reaction score
76
Location
Cornwall
I'm relocating a 16 panel system from a field onto a barn roof. Currently, there are 16 panels, wired as two strings into an isolator. From the isolator there is a two core 4mm SWA which goes underground (about 150m) to the inverter in the farmhouse where it's wired into one of the inverter's two inputs. I've relocated the panels onto a barn roof, and relocated the inverter from a hot loft into the barn instead. This does away with the need for 150m swa run. My question is, is there any reason to wire in two strings as before, as it is easier to wire them together in a single string taking just one pair of wires back to the inverter? Voc will be just under 600v, so well within cable capacity. It's a couple of years since I completed my PV course and have done very little in the way of pv since so just after some gentle reassurance please ;-)
 
Look at the inverter's datasheet to find the voltage limits. Then consider the voltage in cold weather. You'll probably find that you're exceeding the limits so will need to go for two strings.

What inverter and panels are you using?
 
I think most installations are 2 strings or more - so if you have one faulty panel, only one string goes out. You’re still generating something although half of what you should
 
Although they were wired in two strings originally, they were connected in the isolator to a two core swa so in fact only wired back to the inverter as one. I think therefore there'll be no problems with the inverter taking the voltage.
 
I think most installations are 2 strings or more - so if you have one faulty panel, only one string goes out. You’re still generating something although half of what you should

Do you think it's better that way, or isn't it more obvious to the end user that a fault exists if there is no generation at all?
 
You would only notice either way if you watched the inverter output on a daily basis. Unless you have an app that can read it.

Do you have to notify your FIT payee that you are altering the installation?
 
Do you have to notify your FIT payee that you are altering the installation?

Not really altering it,rather just moving it slightly.
Personally,I wouldn't ask the question as you may not like the answer and you cannot really plead ignorance then!
Bit late now anyway seeing as the panels have already been moved.
I suspect they were originally located in the field to get them registered before the FITS cut
 
Although they were wired in two strings originally, they were connected in the isolator to a two core swa so in fact only wired back to the inverter as one. I think therefore there'll be no problems with the inverter taking the voltage.

Were they connected in series at the isolator, if they were in parallel then surely the voltage would have been half before?
 
Were they connected in series at the isolator, if they were in parallel then surely the voltage would have been half before?
Yes, you're right of course! I think the best solution then is to wire them exactly as before. Though it will be pointless using an isolator at the panel end because it's too high up on the inside of the roof to be of any use. I want to bring just one pair of cables down from the roof to inverter so what is the best method of connecting 2 into one? A junction box (or boxes) or mc4 Y splitter?
 

Reply to One string or two? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
431
You need to pass the job on to someone who is competent and up to speed with solar installs and regulations .
Replies
4
Views
669

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top