On my newly commissioned system - 16x Sanyo HIT240 and SMA 4000TL - all has been going well, even to the extent of seeing over 4kW on the inverter dispay a couple of times yesterday and this morning. This afternoon, in good sunlight, I notice one of the strings will never get above 1.8A (about 380v) whereas the other one is regularly at 4 or 5A (around 330v). As a result I've not seen any output above 2.8kW.
The only shading is from the handrail of the scaffolding which is awaiting dismantling, otherwise the panels are S facing with no shade. Can a small amount of shading on about 3 panels cause this sort of differential or is it someone more serious?
Obviously I'm taking it up with the installer but this forum has been a font of wisdom in the past and I'd welcome any thoughts.
The only shading is from the handrail of the scaffolding which is awaiting dismantling, otherwise the panels are S facing with no shade. Can a small amount of shading on about 3 panels cause this sort of differential or is it someone more serious?
Obviously I'm taking it up with the installer but this forum has been a font of wisdom in the past and I'd welcome any thoughts.