What’s the Quickest method of finding exactly where the break in the ring is? It’s on the neutral conductor. Split ring and then join the line and neutral at dB and test between live and neutral at midway on both legs and narrow it down this way?
 
What’s the Quickest method of finding exactly where the break in the ring is? It’s on the neutral conductor. Split ring and then join the line and neutral at dB and test between live and neutral at midway on both legs and narrow it down this way?
Yep best way I know
 
I sometimes do it that way.
Another way, if you are alone in the house, and no-one is watching, and you can unplug everything is to take one end out at the CU and wago each conductor, energise the other end, and then just go around with a socket tester and see what works and doesn't.
If you then do a plug in Zs at the ones that worked, the highest Zs is the closest to the issue.
 
I sometimes do it that way.
Another way, if you are alone in the house, and no-one is watching, and you can unplug everything is to take one end out at the CU and wago each conductor, energise the other end, and then just go around with a socket tester and see what works and doesn't.
If you then do a plug in Zs at the ones that worked, the highest Zs is the closest to the issue.
Or dead test as above but long lead and continuity test from socket adaptor N to one on the N in the DB?
 
Or dead test as above but long lead and continuity test from socket adaptor N to one on the N in the DB?
OK till the customer's poodle gets it's canines into your wander lead.
 

Reply to Open circuit fault on ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Very technical :D
    • Like
Replies
9
Views
517
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
794

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top