I like the idea as I still struggle as to why we live with this risk of open PEN conductors, yes we mitigate by doing PME and inside an equipotential zone you will probably be ok (although people who have received a shock standing on an "insulated wooded floorboard might disagree). Yes why not make it so this fault cannot occur on the network (running a separate earth conductor seems the smartest option for me (true TN-S)) but once again cost is reducing safety (and I guess that all those PME earth electrodes cost less than the extra conductor). Also if PME was a satisfactory solution why would we be having all the fuss with EV charging, Well because it is outside the house, but so are hot tubs, swimming pools, outside lights, deck heaters, bonded outside taps etc. not much new about using electricity outside (I have plastic double insulated outside lights for the exact reason of a PEN fault, as my outside light are very easy to touch.
The Zappi EV charger V2 detects a broken PEN conductor, and does a lot more.
Looks like a really nice EV charger.
There are a few EV charges with "detect" an open PEN conductor the problem is they dont!, The Matte single-phase device disconnects L N and CPC if the voltage is outside of a range, although this offers some protection it is very possible to still have a dangerous situation and the voltage remain within the allowable range due to phase imbalances and extraneous conductive parts (matte themselves even demonstrate this in one of there videos)
The Zappi does not detect an open PEN it does the same as above but with the addition of detecting if someone is receiving an electric shock because of a PEN fault, much like a class one device supplied from an RCD without a CPC, if you get a shock from it the RCD should disconnect but it requires you to receive a shock thats why we have the CPC to enable it to be ADS. That is exactly how the zappi is working it requires a person to receive a shock to disconnect so it is NOT ADS (watch their video where the guy simulates touching a car using a banana lead I wonder why he didn't use his hand !!!), it is better than nothing but not really a solution.
The best solution I have seen is the Matte 3 phase device which has 3 resistors configured in a star configuration between phases, this provides a "virtual" natural point so the difference between this point and the PEN conductor is measured and then disconnection occurs if the difference is above 70v. This device also has ensures all phases are present as a phase loss would stop the device from working properly. This option works well it will not detect a open PEN if the phases are balanced but then there is not a risk of the PEN being a dangerous voltage, This type of device I guess could be implemented on the electrical grid, but not for domestic properties as most houses only have 1 phase
I have been working on another solution, which is not perfect but an idea. Basically a device which does a Ze loop impedance test every 200ms, and if the loop impedance is above the allowable 0.35ohm for TN-C-S is will disconnect L N and CPC, this can detect a PEN fault because if the PEN goes open the Ze will normally rise unless you have exceptional extraneous conductive parts (under 0.35ohm) in which case there is no risk of high voltage on PEN, If the 3 phases are balanced the device should still work as the current will be returning by the other phases so the loop impedance test will be measuring the impedance though the connected loads on the other phases which will hopefully be more than 0.35ohm. So I think this method should be able to monitor for PEN faults on a single-phase installation