When a open r1 conductor is observed on end to end measurements what is a suitable observation to note on the inspection schedule?
Would Co- ordination between conductor and overload device be included because the CCC has now been affected.
Thanks
 
C2 unless obvious what has caused it to be open circuit (eg. if a cable has been snagged and live end open and exposed then would be C1, - IMO)
Either way 'Unsatisfactory'!
 
There is no observation for this type of fault given in the schedule of items inspected in BS7671. That's because such a fault cannot be determined by inspection, only by testing.
Coordination between conductor and protective device is a design parameter. Presumably this design parameter has been met, so this would not be an appropriate box to use.
So there would be an observation made along the lines of - lack of continuity to ring final circuit conductor on circuit number X. But there would be no corresponding tick box on the schedule of items inspected.
In my opinion of course...
 

Reply to Open Ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top