I have a 20m 16mm t & e cable run up boxing through loft and down boxing in ( ref method c) . The new CU I’m coming from has been put in by a cowboy , rough , no certs etc . There is spare ways but I’d rather come of Henley blocks to isol so I’m just signing off my own work . Question is do I fit a 63a rcd at source and an unprotected CU at other end , or preferably a 60a switched fuse supplying dual red CU ? Just bit worried about feed not being red protected ? Any opinions much appreciated
 
I have a 20m 16mm t & e cable run up boxing through loft and down boxing in ( ref method c) . The new CU I’m coming from has been put in by a cowboy , rough , no certs etc . There is spare ways but I’d rather come of Henley blocks to isol so I’m just signing off my own work . Question is do I fit a 63a rcd at source and an unprotected CU at other end , or preferably a 60a switched fuse supplying dual red CU ? Just bit worried about feed not being red protected ? Any opinions much appreciated
Sorry RCD not red
 
Will the submain be within 50mm of the surface of the walls? If so you need a RCD

If not you probably don't.

As for coming off the existing CU ........ your EIC covers what you state, so whats the concern?
 
If twin and earth is installed in or through a partion made from metal frame then it requires 30mA RCD protection...like the metal frame they chuck up for stud work walls on newbuilds.
Or as an alternative to rcd protection by a 30mA rcd, you can use earthed containment or a cable with a metallic sheath connected to earth like swa
 

Reply to Opinions please on 20m 16.0mm run in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top