Ok contractors on site have jointed a existing 4x70 to a new 4x70 to extend onto a chemical process panel and I was testing same today . Phase resistance is .03 and Pe is .10 so all good . I opened j box to discover both cables glanded ok and banjos linked via 10sq and bolted with gutter bolts which I hate as I said they belong on gutters not electrical connections. Then at chemical panel they glanded the cable in panel loose and took a 16sq on the dreaded gutter bolt again down to the earth bar .
So my issues are the gutter bolts , 10 sq and 16 as earth tails which I would myself use a 35 sq as it's half the phase conductor or do you think the 10 16 sq is ok given it length is so small the the resistance in very low . They also intersepted a high level earth bar which was for local bonding and took a 35sq to the chemical panel which did bring the fault loop from .10 down to .03 , what would be your taughts on this .
So my issues are the gutter bolts , 10 sq and 16 as earth tails which I would myself use a 35 sq as it's half the phase conductor or do you think the 10 16 sq is ok given it length is so small the the resistance in very low . They also intersepted a high level earth bar which was for local bonding and took a 35sq to the chemical panel which did bring the fault loop from .10 down to .03 , what would be your taughts on this .