Hello, are there any helpful sparks out there who will answer a question for me? I want to put a 2 way CU into a garage for lighting and a few 13amp sockets but I also want a 32 amp socket for occasional use of a welder. I'm doing the first fix myself as I have the ceilings down anyway.

My plan is to come off the non-RCD protected side of the house CU with a 40amp MCB. I'll run 6mm T&E to the outside via an IP66 junction box on the wall and then 6mm SWA to the garage (voltage drop is not a critical). As I understand it this should comply (even without RCD protection at source) so long as I protect the T&E with an earthed galvi conduit wherever it is less than 50mm deep (even if in a safe zone). Can anyone confirm this?

In the garage I will fit a 2 way RCD protected CU with 16 and 6 amp MCB's, which I understand should give reasonable discrimination with the 40 amp at source, but is it acceptable to fit a large switch before the garage CU to divert the entire sub main to a 32amp socket for the welder. I realize I would have no lighting or heater when welding, but would it be acceptable under the regs to do this?


Regards

Chris
 

Reply to Options for a 32 amp supply to out building in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
476
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
955
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

Similar threads

Are you sure the existing outside socket is on the ring, and not already a spur? I tend to place a switch fuse on the ring inside so that the...
Replies
1
Views
192
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top