The other day I was leafing through the red OSG and for no reason started to read chapter 5, isolation and switching. At point ii for every other circuit it says blah blah blah......... The device must switch all live conductors in a TT system and all line conductors in a TN system.
The latter point I have no problem with. It's the former. Does this mean ( you should read the full paragraph to be honest. I couldn't be bothered to type it!) that in a TT system all circuit breakers should be double pole? It certainly reads that way in my eyes.
I rarely have any dealings with TT systems, so I don't get involved. But one day I may need to know the answer to this. Anyone?
Simon
 
reading between the lines, it is saying that on a TT system there must be the facility for isolating both live conductors, i.e. a double pole isolator, but in a TN system the main switch/isolator can be single pole.
 
the neutral is a live conductor as it carries current , but it is not a line conductor ( phase conductor in english, before the eurotrash interfered)
 
Ackbarthestar. Doesnt matter if its a tn or tt sysyem. All neutrals are live. Disconnect a neutral of an energised circuit at a consummer unit with 23 5ft flu's on it. Then touch it. It's live!

I don't have a problem with a neutral conductor being live since by definition it carries current under normal conditions.
But I think we are not talking about touching a disconnected neutral while the circuit is still energized. That's painful, but after the single or triple pole isolator has been turned off.
 
Hello all.
The other day I was leafing through the red OSG and for no reason started to read chapter 5, isolation and switching. At point ii for every other circuit it says blah blah blah......... The device must switch all live conductors in a TT system and all line conductors in a TN system.
The latter point I have no problem with. It's the former. Does this mean ( you should read the full paragraph to be honest. I couldn't be bothered to type it!) that in a TT system all circuit breakers should be double pole? It certainly reads that way in my eyes.
I rarely have any dealings with TT systems, so I don't get involved. But one day I may need to know the answer to this. Anyone?
Simon
Yes, they should be double pole, if they are intended to be used for isolation purposes.
Unfortunately such devices are very rare in the UK, very common in Europe.
 
OK I may be off track with this, but from your comments due to the potential voltage difference between neutral and earth on a TT system a MCB should break both the line and neutral. I can see the logic of it. So are all recently install 17[SUP]th[/SUP] edition boards on a TT systems technically wrong then?

Out of interest are RCBO’s PD or SP?

Now how do you convince the customer that you fitted a nice shiny new board for last week that he now needs a new board!

Europe strikes again! We’ll end up with those monstrous DP boards!
 
Interesting post.

If you look at pages 24-26 as well, the suggested diagrams also seem to contradict that which simonspark has pointed out, as in, they show the layout of every new TT board in the country as Tony points out (btw Tony RCBO's are single pole .... ? 99% anyway).

I have also seen the double pole MCB/RCBOs in a french made van :)

They look a bit like a contactor with tiny little terminals. And a switch on of course.

So not like a contactor at all.



I wonder what the answer to this is. Maybe its just that they are guidelines and this particular one has fell by the wayside (apart form their being a DP isolator up front).
 
The Regs allow us to isolate a group of circuits for isolation, its for the designer to make a risk assessment and consult with the client and decide on how safe isolation shall be achieved. If this was a say a working farm how convenient and safe will it be to isolate a group of circuits. For safety and for minimal disruption individual circuit isolation may be appropriate or it may not.

Regards Chris
 
Until the thread it’s something I’d not considered. There is the possibility of a considerable PD between neutral / earth. It does throw even more reliance on to the RCD, which I’m not keen on in the event of a fault. With a line / earth fault you have the MCB to back up the RCD. A neutral / earth the entire fault is in the RCD’s domain, and considering the PD a large fault current can ensue. DP MCB’s are beginning to make sense now.
With the number of faulty RCD’s you guy’s report I wouldn’t be happy.

Just glad I don’t live out in the sticks now.
 

Reply to OSG. Page 33. Is this right? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
164
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
682
N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top