Hi

We are having a new log cabin installed at my work place and after some advice. Will be getting electrician to come and quote etc but would like to know what it entails first if possible.

Currently we have one cabin (with lights, sockets, heater) this is fed via a 2 way garage DB - 40A, 63A RCD main breaker - 15meter run SWA. This 2 way DB is fed from a main DB in another room fed from a 40A MCB also. Im guessing the cable sizes are 10mm maybe 6mm. My question is can i feed another log cabin 50meters away (needing lights, sockets, heater) using SWA and another 40A MCB in the 2 way DB?

What would people suggest?

All advice info appreciated

Thanks
 
An assessment of the new load (allowing for diversity) upon the existing needs to be done first. As long as this and other checks have been done and there is suitable space in the existing D.B. the principle should be the same albeit the distance is greater, therefore, the cable supply is bigger.
 
Has anyone used any other methods of routing SWA cable outdoors?

Ive only ever known used burying cable 600 deep, sand base, tape etc.

But my boss is not happy with the price, especially for the ground works side, and wants me to explore other ways.
 
Also the other option is traywork depending on route and aeshetics of the building.
 

Reply to Outdoor Cabin Feed Help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
958

Similar threads

  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
318

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top