Hi Guys,
I need to supply the gate control fitters with a 10a supply for the control of some new electric gates im having fitted.
The supply would be on the outside wall of what is my Dining room.
My plan is that I was going to come off of an existing double socket into a new fused spur set flush next to the socket.
next I was going to go out of the rear of the fused spur through the wall and terminate in a rotary IP66 20a rotary isolator.
The fused spur would be 13a fused and the cable 2.5mm T&E.
Can you see any problems with this?
I should add I am an Electrician just never done domestic and so no 17th edition etc.
Yes I understand it should be done by a part P but why when I'm more than capable?