Hi guys
Wanting to put an 8 watt led light fitting outside ,
Only place I can get a supply from is kitchen ring main got a radial approx 4th long.
now issue is the radial is already feeding combination boiler and a single socket for washing machine. If I put additional spur in for outside light am I getting to close for maximum load as like I said already got 13 amp for washing machine and 3 amp for boiler so with outside light with 3 amp fuse in spur then load going to be 19ampeven those new lights won't be pulling 3 amp tia
 
Sorry 4mtrs long radial off of a rfc supply to a kitchen with 32amp mcb,
The radial currently supplies single one gang socket outlet to washing and fused spur to combine boiler,
Assuming the radial will carry 20amp safely?
 
washing machine will be no more than 10A when heating. just add a FCU with 3Aor 5A fuse for your outside kight.

Was so much better when washing machine had a hot n cold fill..
With the option of economy wash to bypass the heating stage of the wash..
Apparently, it’s more economical to heat cold water than to use stored hot water
 
Hi barnaby I'm unsure but I will test the circuit and see how I get on with results, assuming ill need to do a zs and ir test and compare again on site guide
Thanks guys for your replies was more just wanting confirmation that would be okay loading it up a bit more, provided I'm under 20amps
 
Couldn't see why you were talking about rfc and radial when only one circuit involved. It's all on one spur from the ring, I take it.
 

Reply to Outside light off an already used spur in 2.5t&e in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
768
When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Replies
2
Views
429

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top