Hi guys
Wanting to put an 8 watt led light fitting outside ,
Only place I can get a supply from is kitchen ring main got a radial approx 4th long.
now issue is the radial is already feeding combination boiler and a single socket for washing machine. If I put additional spur in for outside light am I getting to close for maximum load as like I said already got 13 amp for washing machine and 3 amp for boiler so with outside light with 3 amp fuse in spur then load going to be 19ampeven those new lights won't be pulling 3 amp tia
 
Hi no its a 2.5 radial of a rfc either out of a socket outlet or joint box but I can't get to find it . so I've got a radial into a single socket outlet with washing machine into it then into a spur for boiler
no such animal Gary its a spur off an RFC which in turn feeds another spur, A radial will be fed from its own OCPD
Yes I've looked at appendix 15 and as uve said doesn't comply so won't be doing that then thanks for all the advice guys appreciated! !!
uve??
 
Hi guys
Wanting to put an 8 watt led light fitting outside ,
Only place I can get a supply from is kitchen ring main got a radial approx 4th long.
now issue is the radial is already feeding combination boiler and a single socket for washing machine. If I put additional spur in for outside light am I getting to close for maximum load as like I said already got 13 amp for washing machine and 3 amp for boiler so with outside light with 3 amp fuse in spur then load going to be 19ampeven those new lights won't be pulling 3 amp tia
Just say no
 
No point putting a fcu at start of radial/spur due to fact it's already feeding washing machine and then a fcu for boiler if I then add a fcu for light then probably getting too close to fcu rating and can't get to connect to lighting circuit so don't see can be done . But can't win them all lol
Only 1 QNE non fused spur is allowed from an RFC so in this case It should have been spur at the origin via an FCU see appendix 15 BS 7671 for info
 

Reply to Outside light off an already used spur in 2.5t&e in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
783
When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Replies
2
Views
441

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top