A circuit is defined by:
'An assembly of electrical equipment supplied from the same origin and protected from overcurrent by the same protective device/s'
so anything being supplied from a FCU is being supplied from the same origin and protected by the same PD. ie. the origin of that circuit is the FCU.
A Final circuit is define as:
'A circuit connected directly to current using equipment, or a socket outlet or socket outlets or other outlet point for the connection of such equipment'
ok. so it is a final circuit. Good so far
Device/s being the operative word
No sure what you mean here. We have a single protective device (the FCU). Your not saying all DBs have to have more than one PD are you?
So the protection of the circuit is by the OCPD at the origin.
Origin of that circuit yes. Not necessarily the origin of the installation which would of course rule out sub boards completely.
If you consider the origin to be at the consumer unit then the rfc includes both the spur and its BS1362 fuse; if on the other hand you consider the circuit to be directly connected to equipment as defined by a 'final circuit' then you would only look at the spur at the point where it starts, that is, the SFCU.
We would then record our results on our MWC or, as possibly defined, an EIC , being a new circuit.
Suits me
However, we know that when measuring the R1+R2 and subsequently the Zs of a rfc we take account of any spurs, fused or unfused, and use the maximum value as our Zs.
True, but so what? I'd argue that we do this because it would be a pain to treat every fused spur as a separate circuit, both from a design and testing point of view. However it doesn't mean we have to do it that way! If the spur meets the max Zs of MCB in the main DB then great. I am just arguing that if it doesn't we still have the FCU fuse to fall back on.
Additionally, would a flexible cable supplied by a plug and socket clipped to a structure supplying equipment be regarded as a final circuit requiring a separate EIC?
No, because the regs only deal with fixed wiring. Anything beyond a socket doesn't count
So I must veer towards Tel's argument on this one.