looking for a bit of info
went to look at a job today sorting outside lighting, the cut out is a mess. The swa are not terminated using glands and instead earth clamps round the exposed armouring. It is a tnc-s supply and am sure i have seen it some where that the end light should have a rod connected to it, although i can not find this in the regs. What i did find that reg 559.10.3.4 requirea a mimimum copper equivilent conductor not less than 6mm. It only has a 2.5mm2 3 core and the swa works out at about 2.4mm2 something copper equivilent conductor.
Any ideas cheers:rolleyes4:
went to look at a job today sorting outside lighting, the cut out is a mess. The swa are not terminated using glands and instead earth clamps round the exposed armouring. It is a tnc-s supply and am sure i have seen it some where that the end light should have a rod connected to it, although i can not find this in the regs. What i did find that reg 559.10.3.4 requirea a mimimum copper equivilent conductor not less than 6mm. It only has a 2.5mm2 3 core and the swa works out at about 2.4mm2 something copper equivilent conductor.