looking for a bit of info

went to look at a job today sorting outside lighting, the cut out is a mess. The swa are not terminated using glands and instead earth clamps round the exposed armouring. It is a tnc-s supply and am sure i have seen it some where that the end light should have a rod connected to it, although i can not find this in the regs. What i did find that reg 559.10.3.4 requirea a mimimum copper equivilent conductor not less than 6mm. It only has a 2.5mm2 3 core and the swa works out at about 2.4mm2 something copper equivilent conductor.

Any ideas cheers:rolleyes4:
 
if the L and N conductors are 2.5mm, then the cpc need not be more than 2.5mm. IMO. the terminations need sorting though with proper glands.
 
559.10.3.4 : The Earthing conductor of a street electrical fixture shall have a minimum copper equivalent CSA of not less than the supply N conductor at that point or 6mm^ whichever is the smaller
 
when you say the cutout is a mess is is a proper street lighting cutout? these sometimes just have a brass cone on which the armoured goes over and indeed is clamped on with a pipeclamp type band
Street Lighting Cut-Outs
 
Last edited by a moderator:
jase beat me to it, while i was making a sarcastic comment on another thread. as i said in post #2, same size as L/N conductors is compliant. the 6mm comes in where the L/N conductors are >6mm
 
What i'm thinking about, is if these are pole mounted lighting units, then the metal poles may well be extraneous, being set in the ground in a concrete base, and could well need a bonding conductor linking these posts out on a PME supply...
 
cheers guys

it is small private lamposts in a car park with 2 x 70w sons. They are not glanded of and not restrained ( only thing that is holding them in place are the terminations). originaly went to change lamps and noticed it when pulling out the cut out fuse
 
What i'm thinking about, is if these are pole mounted lighting units, then the metal poles may well be extraneous, being set in the ground in a concrete base, and could well need a bonding conductor linking these posts out on a PME supply...

was thinking along the same lines. I know i have seen a bit about a rod at the end one. Not sure if its in GN8 which i dont have at hand right now. Hench why i asked you kind fellows
 
was thinking along the same lines. I know i have seen a bit about a rod at the end one. Not sure if its in GN8 which i dont have at hand right now. Hench why i asked you kind fellows


Then i would first test these poles, (you haven't confirmed or otherwise if these are pole mounted lighting?) to find out if they are extraneous or not. If they, are it would be far easier to TT these poles than to provide a bonding cable!!

EDIT ...sorry i missed the post where you confirmed they were posts ...lol!!
 
Last edited by a moderator:
was thinking along the same lines. I know i have seen a bit about a rod at the end one. Not sure if its in GN8 which i dont have at hand right now. Hench why i asked you kind fellows

It doesn't matter too much where the TT rod is installed, so long as all the posts are connected via the SWA from the post position where the Rod is connected too!! Don't forget to isolate the incoming supply SWA, as that will still be at the house PME potential...
 
Last edited by a moderator:
There does not seem to be anything specific for street furniture in the regs.

5 second disconnection time for the distribution circuit (TT or TN)

Should be RCD'd (locally)

Only (the frame etc.) needs earthing if non-sheathed cables are used or class 1 fittings are used.

having said that I only have the 'old' GN8, as I haven't got the new revised copy
 
Last edited:

Reply to Outside lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

Ask your electrician when they do a site visit as to what is required they can also notify the installation to Building Control under Part P of...
Replies
1
Views
455
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top