Ok i may get slated for this one but here goes; A bit of background info first.
Its been a while since ive looked at my iee regs, and ive not done my 18th edition but get the updates. i no longer practice much electrical due to a career change.
But for friends, family old customers when i get time i still do the odd little job.
I have been asked to install an outside socket which normally is never an issue just to spur of an internal socket.
This time ive been asked to install a socket 6m away for one of those inflatable hot tubs.
As i remember the regs state you can spur off a socket in 2.5mm t&e im sorry but i dont recall it ever mentioning lengths.
Now a 2.5mm twin and earth is only capable of 25A approx if you plug in two 13A sockets thats 26A. That all works but are we forgetting its on a 32A MCB that cable would burn out before the mcb trips if there was an overheating issue?
Im pretty sure the 6m is not that much of an issue. but if i do a cable calc for this little job it says the cable should be 4mm, im assuming due to the 32a mcb.
Im contemplating installing a XLPE SWA 2.5mm² 6943X 3 core to a single socket, the cable being rated at 31A and a single socket at 13A.?
So putting all the questions to one side and working on the above assumptions.
Would you install a 2.5mm or 1.5mm armoured or a 4mm?
To either a single or double socket?
to be safe than sorry and to future proof i could just install a 4mm to a double socket!!
Its been a while since ive looked at my iee regs, and ive not done my 18th edition but get the updates. i no longer practice much electrical due to a career change.
But for friends, family old customers when i get time i still do the odd little job.
I have been asked to install an outside socket which normally is never an issue just to spur of an internal socket.
This time ive been asked to install a socket 6m away for one of those inflatable hot tubs.
As i remember the regs state you can spur off a socket in 2.5mm t&e im sorry but i dont recall it ever mentioning lengths.
Now a 2.5mm twin and earth is only capable of 25A approx if you plug in two 13A sockets thats 26A. That all works but are we forgetting its on a 32A MCB that cable would burn out before the mcb trips if there was an overheating issue?
Im pretty sure the 6m is not that much of an issue. but if i do a cable calc for this little job it says the cable should be 4mm, im assuming due to the 32a mcb.
Im contemplating installing a XLPE SWA 2.5mm² 6943X 3 core to a single socket, the cable being rated at 31A and a single socket at 13A.?
So putting all the questions to one side and working on the above assumptions.
Would you install a 2.5mm or 1.5mm armoured or a 4mm?
To either a single or double socket?
to be safe than sorry and to future proof i could just install a 4mm to a double socket!!