Hang on - I'm getting confused here. Just noticed your original post mentions 6mm T&E now you're talking about 10mm?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Oven and Hob Cable over current protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes, but only if you put it on a 16A breaker.
And it would have to be a very short run as you would very quickly run into volt drop problems. In reality no one would do it.
My original question wasn't really about diversity. It's about having a 10A (without diversity) oven connected to a 32A 10mm supply. Does it need to be fused down, or is overload of the cable unlikely enough that this isn't required?
any cooker ive connected 1 cable, squeeze them in 1 isolater lol ive lot to learn
rryles , sure your not a window cleaner
The breaker is there to protect cable. If you go down at the outlet to something that can't handle 32A then you would need to put a fuse in.
I thought as much, but hoped otherwise. Maybe I'll be lucky and the oven will come with 4mm flex.
Just to check - I can fuse down using an FCU, or a BS1363 plug and socket?
I presume connecting a 2.4KW oven into the kitchen ring would be frowned upon? I seem to recall anything over 2KW should be dedicated circuit. Just want to be clear on all the options.
I thought as much, but hoped otherwise. Maybe I'll be lucky and the oven will come with 4mm flex.
Just to check - I can fuse down using an FCU, or a BS1363 plug and socket?
I presume connecting a 2.4KW oven into the kitchen ring would be frowned upon? I seem to recall anything over 2KW should be dedicated circuit. Just want to be clear on all the options.