HappyHippyDad
Supporter
Gloucestershire
I have just been asked by a customer if he can just plug his new cooker into a socket. I have said 'No' it needs to be on a dedicated circuit..
I then thought I'd do a bit of research as its only a 2.5kW oven and wanted to see it in black and white in the regs.
I didn't ecpect the Electricians Guide to the Building Regulations (Page 55 - 4.4) to say
"For lightly loaded circuits ovens of rating 13A or less may be connected into a ring final circuit"
Not sure if his kitchen is on its own ring, but if it is I guess its ok to plug in the oven?
Just doesn't seem right, especially after seeing all of Jason's entrys about having to be 2kW or less?
ps... I'll make this my last post for a bit, getting a bit carried away and a bit addicted to this electrics lark ...:rolleyes4:
If there an unused cooker outlet you could change it for a single socket and plug the oven into that,then you will have a dedicated circuit and the customer can use the existing cooker switch to turn it on and off if they so wish.
Just thought I'd finish the thread. The original oven was plugged in, the new oven stated that it could have a plug fitted fused to 13A so thats what I did. The hob was confusing! It had 2.5mm flex on it and stated that it needed to be fused down to 23A (it was 5000W). The 45A cooker switch fed both oven and hob and was run with 6mm cable protected by 32A MCB.
I have removed the flex on the hob and connected the 6mm (that was previously feeding the last hob)directly into the new hob as there were 32A terminals in a box fitted into the underneath of the hob.
I didn't like taking off the flex as that is what it came with but I have to admit that I didn't know how to fuse down to 23A - I cant change the MCB as it feeds both oven/hob and needs to be 32A. Is there a FCU that is greater than 13A??
You can get a 25 amp MCB and put it in an enclosure, ideally you need two supply's 1 for the oven and 1 for the hob . Don't think you should have that 2.5mm flex protected by 32 amp MCB its max current carrying capacity of flex is 25amps
Reply to Oven connected into ring - EGBR says this is ok? in the UK Electrical Forum area at ElectriciansForums.net
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...