I've just been to change an oven tonight, should have been a straight swap.
Large cooker isolator, fine, MCB at 32A, no RCD protection. Not brilliant, but OK for a like for like.
Isolate, remove oven, then find the old oven is plugged into a double socket, with the hob ignition in the other plug.
Hmm, this is not right, so, I check the new oven, and see if it is rated low enough for a 13A plug fitting. No way, maximum demand 3.5kW, and Installation instructions say must be on a DP fused connector.
So, I'm going to have to fit a FSU, well 2 actually, as the hob needs sorting too. Then, because I'm modifying the circuit, I'll have to give it RCBO protection (cable <50mm).
*This is getting complicated for what should have been a 20 minute job.
Firstly, with a 3.5kW rating, the fuse needs to be 15A to cope with max demand. I cant say I've ever seen a 15A fuse. Use a 13A?
Is my thinking correct in this - it must be done right as it is a rented property.
Ta
Alan.
Large cooker isolator, fine, MCB at 32A, no RCD protection. Not brilliant, but OK for a like for like.
Isolate, remove oven, then find the old oven is plugged into a double socket, with the hob ignition in the other plug.
Hmm, this is not right, so, I check the new oven, and see if it is rated low enough for a 13A plug fitting. No way, maximum demand 3.5kW, and Installation instructions say must be on a DP fused connector.
So, I'm going to have to fit a FSU, well 2 actually, as the hob needs sorting too. Then, because I'm modifying the circuit, I'll have to give it RCBO protection (cable <50mm).
*This is getting complicated for what should have been a 20 minute job.
Firstly, with a 3.5kW rating, the fuse needs to be 15A to cope with max demand. I cant say I've ever seen a 15A fuse. Use a 13A?
Is my thinking correct in this - it must be done right as it is a rented property.