Electrician Jobs Oven switch isolator is missing, C2 on EICR

This electrician job is going for grabs, please don't post contact details in this area of the forum. Use the forum messaging system instead.
A always note it on an EICR if there is no appliance isolators
If I want to prove a point I download the installation manual for the appliance - these almost always state an isolator with a 3mm DP contact switch is required.
As manufacturers instructions over ride the regulations then it is a warranted observation.
IIRC it says something on the onsite guide about appliance isolators in kitchens , but I cant be bothered to go to the van as it is raining outside (book in van)
 
I don’t believe Manufacturer’s instructions do override the Regs.
I think you’ll find it’s back to being taken account of?
 
I have not got the new regs to hand (office needs a tidy)
The previous regs had
Section 134 ERECTION AND INITIAL VERIFICATION OF ELECTRICAL INSTALLATIONS
134.1 Erection
Regulation 134.1.1Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation, Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.

PART 5 SELECTION AND ERECTION OF EQUIPMENT
CHAPTER 51 COMMON RULES
510.3 Every item of equipment shall shall be selected and erected so as to allow compliance with the regulations stated in this chapter and the relevant regulations in other parts of BS7671 and shall take account of manufacturers' instructions.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Igor Taranenko,
Last reply from
baldelectrician,
Replies
49
Views
19,431

Advert

Back
Top