H

hightower

Brother got his oven cleaned yesterday, today it's tripping the RCD (not the breaker) - I'm gonna head over tonight and take a look for him but just thought I'd post here and ask for advice/possible things to look for.

Thanks,
 
Had another customer that wanted their 'new' oven fitted a few years back. I upended it to get to the terminals and must have been half a pint of dirty water came out. Perplexed I spoke to the customer. Turns out they got it from their brother. His house was one of the unlucky ones in the Morpeth floods a few years back, and yep, the oven was flooded too! I then suggested that Curry's would probably have some good deals on!
 
I worked in a few of those.
One insurance company would only allow the base units to be changed one of the kitchens as the top units were not damaged lol.
They had to concede in the end though.
 
Well, it seems you've done it again you bunch of legends. Told brother to direct a fan heater towards the oven for a half hour. Turned on without tripping after and he's now been running the oven for a couple hours to try and dry it out thoroughly.

Glad all sorted mate. Think I deserve some lovin tho for #9!! Cmon HT!!

Much much much more importantly though, make sure your brother cancels the spark who's coming round later. It's Friday afterall, should be going home early!!
 
Glad all sorted mate. Think I deserve some lovin tho for #9!! Cmon HT!!

Much much much more importantly though, make sure your brother cancels the spark who's coming round later. It's Friday afterall, should be going home early!!

Everyone gets some lovin. I mean, who would have though you put a bunch of misfits together on a blue and yellow webpage, and they produce something as awesome as this place.

Anyway, yeah, I've told him not to be a p**** and make sure he tells the guy. I think thanks are in order to the cleaning company too as I thought it was a pretty professional response.
 

Reply to Oven Tripping RCD Since Cleaned in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
638
davesparks
D
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top