quite frustrating as a client purchased a 16a oven.

32a ring supplies 13a fused spurs for the old ovens.

I can’t downgrade the MCB to a 20a because the microwave will trip with the oven on.

How can I fuse the 20a ovens locally by replacing the 13a fused connection units.

I am quite sure there is no other way?

I don’t want a mini DB
 
so can you allow for diversity. i.e you can't have oven and grill on at same time? also, the stat. will be switching I/O so the max load will only be for short periods. does the oven come with a fitted plug? if so try it and clamp the circuit, see what it pulls.
 
New 20 Amp Radial required I reckon Chris. Davesparks is right, always been a recomendation only that anything over 2KW should be on it's own dedicated circuit, this will be where the arguments start, mark my words, some will say rubbish, but common sense should prevail.
 
How about swapping out the 13a switched FCU for a 20A dp switch? As long as it is at least a 2.5mm on the outgoing.
We don't do things like that here in the UK! Being a cowboy may be OK where you come from but not here.
Loads greater than 2KW should be on their own circuit.
 
We don't do things like that here in the UK! Being a cowboy may be OK where you come from but not here.
Loads greater than 2KW should be on their own circuit.

Oven is 16 A, so only using 50% of the circuit capacity, so how many points is this circuit feeding? And if 2kw load need a dedicated circuit, then what are these 13A fused spurs about, I might have spurs on my cowboy boots, but by my calculations a 13A fused spur at 230V means you are tapping 3kw branches off an existing ring?
 
Oven is 16 A, so only using 50% of the circuit capacity, so how many points is this circuit feeding? And if 2kw load need a dedicated circuit, then what are these 13A fused spurs about, I might have spurs on my cowboy boots, but by my calculations a 13A fused spur at 230V means you are tapping 3kw branches off an existing ring?
Where does it say anythinover 2Kw needs a separate circuit? do you have a Regulation Number I can refer too? An English Regulation not a NEC one.
 

Reply to Oven trouble need larger than 13a in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
368
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
542

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top