Evening all...just a quick question. A customer was using a wallpaper stripper on a ring circuit, smoke started coming out of the back of the socket before the 32amp breaker tripped, what I don't understand is why the 13amp fuse in the plug didn't break? Could someone tell me why? Thanks
 
Steam cools,water acumalates behind socket,tracking between L+N or E ( no rcd) breaker current exceeded and out it goes
Plug top fuse intact because there is no excess current after the socket terminals
 
Fuses dont operate as fast as MCB's.
Now I dont have a BGB to see how fast a 32A MCB operates and at what current but Apparently a 13A Fuse is required to operate at 1.9 times rated current (24.7A) within 30 minutes.
So if its operating at say 40A it may take 15mins to blow where a MCB will probably operate faster.

Did you find what caused the fault?
 
Ive see temperatures in switch gear weld the terminals and cables yet the heat damaged HRC fuses don't operate..... the current needed to operate the fuse-wire needs to get it white hot, so in principle heat generated by a loose connection may not get anywhere near the same temp that is needed to melt the fuse wire.... when you've seen fuses glowing red without operating its an headscratcher the first time ....same principle applies with plug-top fuses.
 
If its any consolation, i went to a tripped 32A socket MCB which was caused by a coiled up extension reel feeding a 2KW heater. THE 10AMP fuse on the reel plug head was still going strong.......

Pffttt thats nothing!
We had a fire alarm go off caused by 2x 3kw heaters plugged into a 25m rolled up lead.

It was a pile of PVC mush and coper when i got to it LOL
 

Reply to Overcurrent in circuits in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
397
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
2
Replies
15
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top