Hi all, I'm fairly new to all this so bear with me if it's a ridiculous question...

In my text book that I'm studying for my course (c&g 2365) it has symbols that you use to define whether the protective device will work for a given circuit (I think? please correct me if I'm wrong).

The symbols are
Iz (current carrying capacity of conductor)
It (value of current stated in regs for type of cable and install in amb temp of 30c)
Ib (current intended to be carried by circuit)
I2 (operating current of protective device)

Then it gives me a formula of conditions that must be satisfied for circuit

Ib<In<Iz and I2<1.45 x Iz

Where does the In come from? Am I being stupid?
And also how would you work out much current appliances and cookers will use on a circuit?

Thanks
 
In is the rating of the fuse/MCB. so that Ib<In (so the ocpd won't trip zt normal load). and In< Iz ( so that the ocpd will trip before the cable is overloaded). I2 is the current which will cause the ocpd to trip ( as ocpd's will stand overload. I2 is generally 1.45 x In).
 
Hi all, I'm fairly new to all this so bear with me if it's a ridiculous question...

In my text book that I'm studying for my course (c&g 2365) it has symbols that you use to define whether the protective device will work for a given circuit (I think? please correct me if I'm wrong).

The symbols are
Iz (current carrying capacity of conductor)
It (value of current stated in regs for type of cable and install in amb temp of 30c)
Ib (current intended to be carried by circuit)
I2 (operating current of protective device)

Then it gives me a formula of conditions that must be satisfied for circuit

Ib<In<Iz and I2<1.45 x Iz

Where does the In come from? Am I being stupid?
And also how would you work out much current appliances and cookers will use on a circuit?
Thanks

In = nominal rating of overcurrent protective device.

appliances usually come with the Kw rating attached. use the formula I = P/V to work out the current demand. remember to apply diversity where allowed.
 
Thank you very much! That makes much better sense. Became pretty obvious once you said it! Haha
So if you have numerous appliances on a circuit is the total current all of them added together?
Thanks again!
 

Reply to overcurrent protection question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

  • Question
You don't normally see It in the equation. What you would normally do is apply correction factors then select a cable/conductor for Iz from It...
Replies
7
Views
559
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top