overhead incoming supply TT TNCS? | on ElectriciansForums

Discuss overhead incoming supply TT TNCS? in the UK Electrical Forum area at ElectriciansForums.net

J.C.E

-
Arms
Joined
Dec 2, 2010
Messages
832
Reaction score
165
Location
Earth
Looked at a rewire for a 5bed house reno this morning
bit of a odd setup!

so the house is supplied overhead- see pic 1- 2cores through the roof in loft
into a 60a fuse
then what looks like a 16mm T+E- but cpc (if one) is not used
this travels some meters (at a guess 10m) down to the ground floor- appears to be clipped as apposed to burried in wall.

this then goes into a 2nd 60a fuse (see pic 2)- see a 16mm G/Y cable- joint to the neatral- acting as the main earth.

the ze reading at the c/u is 0.22 with the main bonding dissed

few points:

1)the 20m run from loft to ground floor is un-metered and should be RCD

2)the wall that the 2nd 60a fuse+meter+c/u is planned to be knocked down anyways- so he needs me to remove electrics from there

3)am I right is saying this is a TNCS due to the reading- although on first impressions assumed a TT overhead?

4) would be acceaptable- to get rid of everything and start again-
so head in loft>> meter right next to it>>into new switch fuse iso>> swa sub main into a new consumer unit in a more accessible cupboard on 1st floor

[ElectriciansForums.net] overhead incoming supply TT TNCS?


[ElectriciansForums.net] overhead incoming supply TT TNCS?


[ElectriciansForums.net] overhead incoming supply TT TNCS?
 
I'd be requesting the DNO to come out and sort out their supply. I doubt they'd go for a meter in the loft due to access even if they fit a smart one.
 
If you did max demand on that box alone, then add whatever the submain is supplying seems like quite a load. Is that lead covered the supply cable in the loft?
 
Last edited by a moderator:
Ok so those two black cables go to the off peak supply/timer Think I can just see the PME label under the tails but isn't that supply to off peak the wrong side of the meter? Oh yeh can see the label above now, just ignore me.
 
Last edited by a moderator:
Where does that black cable go to under the earth cable in the fused connection? Doesn't look like TN-C-S If it's overhead you would think TT but then how is that earth to consumer unit supplied. If you did max demand on that box alone, then add whatever the submain is supplying seems like quite a load. Is that lead covered the supply cable in the loft?
goes into that meter on the ajoining wall

then 16mm cable did look like lead- and had that black stuff twisted around the end
 
Ok so those two black cables go to the off peak supply/timer then maybe they did allow TN-C-S there then. I have had it agreed before to do that by the DNO in more remote places with TT.
they are actually having a loft ext- that side of the roof is not changing- will just be boarded over- but it will be more accessible than it just being a attic- then I could suggest a access panel to the meter and head
 
If you did max demand on that box alone, then add whatever the submain is supplying seems like quite a load. Is that lead covered the supply cable in the loft?
the sub main is a 2nd c/u on 1st floor
think it was previously 2x flats- but it will now be one house- max demand wise- 60a will be fine- minmal points, gas cooking, gas CH
 
The cut out by the meter should be a RED link as the main fuse is in the loft. Moving the meter would be down to supplier and Dno agreeing.

Can’t see how it can be PME as no earth at head in attic. So it would have to be TT.

Looking clearly it is PME but if wall is being taken out DNO need to be called to move supply, and should fit a nice new series 7 or 8 cutout. Correctly labelling and identifying what earth you have.
 
Last edited:

Reply to overhead incoming supply TT TNCS? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top