Greetings.
I am helping to re-wire a bungalow that has an earth rod.
The supply cable is overhead, it's the same for the whole street.
I took a walk up the road and noticed all the overhead cables converged on one single pole.
On the pole was written PME and three cables ran down the pole into the ground, I am assuming these cables are supplier earth rods as they didn't look fat enough to be power cables.
I spoke to a friend and he said it looks like the supplier is going to upgrade the whole area to PME in time.
However I was told at college a while back in 16th edition that overhead cables should be earthed via TT system because overhead cables are more likely to suffer a neutral fault and hence you would lose your earth aswell. I was told this a while ago and I could have got this fact wrong.
So my question is if the supply is overhead is it better to use a TT system or to use a PME system?
I just wonder what would be the best earthing arrangements for this scenario.
I understand that any TT system must be RCD protected to max.
Thanks.
 
Last edited:
No need if an insulated CU is used. :)

Ooh nice.

Mind you, I think I will still use one for safety, TT earth fault loops can be high and as discussed RCDs can fail, I prefer to have that back up and I always price them into TT jobs anyway. Come to think of it, I may start putting them on all installations. It can't hurt, right?b
 
Rocker

If you had a metal clad consumer unit,as long as the tails are bushed at entry theres no requirement
Only just reminding you that if you fit an 100m/amp Rcd it would have to be time delayed and they are around ÂŁ 80 a pop
 
can only hurt the customer's pocket! i certainly wouldnt bother if the tail's are in good condition and it's not in a area likely to get fiddled with by kids etc. RCD's can fail hence the quaterly test's that no one ever does!
 
Think you have a choice of mA value depending on Zs (table 41.5), although if you have 2 rcds you have to ensure discrimination (411.5.3).
I think 100mA for the upstream RCD is sensible to minimise nuisance tripping. Not sure about circuits over 32A:confused:
 

Reply to Overhead supplies?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
191
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
That traffolyte label glued to the service head is the same as those screwed to the wooden support poles.
Replies
10
Views
507
Hence the former name for TNC-S, PME. Protective Multiple Earth.
Replies
5
Views
806

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top