no, not my brain overloaded, but it's getting there. called out to a pub, regular customer. problem is his pub kitchen load. situation is:;

Main DB supplies most of the pub circuits - individual MCBs. 4 63A MCBs each feed sub-DBs. Main Board is full, no spare ways.

Problem is the main kitchen DB, a 10 way square D. is pulling, when the kitchen is up and running, 65A + through the 63A Type C MCB in the main DB. This MCB is tripping, obviously , depending on stats. switching and excessive load, the current is just too much.

The feed to the kitchen DB is in 16mm, and at the 60+amps, it's temperature is 39deg. it's surface clipped,about 10 metres.so a short answer would be to push the MCB to 80A, but this is getting close to overloading the 16mm, and there is not an 80A MCB made ( it's a memshield board.

Short of a major wiring job, I can't see an easy solution.

I'm going down today to see if there's any way of diverting some of the kitchen load to another DB that is'nt so heavily loaded, and look at the option of splitting the tails at the main DB and feeding the problem kitchen via a switch fuse. just concerned if I can protect the 16mm feed at 80A without overloading it.
 
Last edited:
T Bone is that all at least a 32 oz er
that's the one with all the chips and all. back to the job. plan is to divert one high load appliance fromoverloaded board to a 45A D/P isolator ( not in use but wired to supply from other board) copex and 6mm singles, only about 3m run, check olads again and if necessary divert another to second disused isolator. this should shift between 30 and 50A to the under used board. then it's up to the landlord, the brewery and manweb to sort out the supply side. if they go for 3 phase, it's a bloody long trench from wrexham.
 
DNO have already replaced the neutral conn. caught fire a few weeks ago. it's not a normal head. 2 supply tails about 70mm into separate boxes. looking at the green deposit on what i can see of the tail ends. no way am i even going to try and get the cover off. not my problem.
 
Last edited:

Reply to Overload Help in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
734
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top