Hi can someone help me with this situation please.

The service head/meter is in a brick built housing box in the middle of a field, we are running power to a house some 40m away from it and im not sure of the most suitable method of protecting the 25mm SWA cable from overload. The DNO fuse is 100A and ideally would like to have 100A at the house. Can I safely use a 100A type C MCB in a small consumer unit at the origin? or is there a better way? I cant reduce the supply to 63A and go with a type B mcb as this wouldnt be sufficient.

Thanks

Simon
 
Hi can someone help me with this situation please.

The service head/meter is in a brick built housing box in the middle of a field, we are running power to a house some 40m away from it and im not sure of the most suitable method of protecting the 25mm SWA cable from overload. The DNO fuse is 100A and ideally would like to have 100A at the house. Can I safely use a 100A type C MCB in a small consumer unit at the origin? or is there a better way? I cant reduce the supply to 63A and go with a type B mcb as this wouldnt be sufficient.

Thanks

Simon
You're stuck between a rock and a hard place with this. From a purely electrical perspective the DNO fuse provides the overload protection, however there is the fabled 3m rule which says you need to provide a CPD and some discrimination. Your quick option would be an 80A KMF, there isn't really anything between that and 100A. If you want to get as close to 100A as possible just not quite (and I'd be intrigued on a domestic, but that's another story...) then you need to look at electronic adjustable MCCB's and then you're into big money.
 
Off the cuff I can tell you the cable is well undersized for your needs.

You need to establish the installation method, we already have the length and cable type so you then need to apply cable calc's to establish the recommended cable size for this run to ensure your VD is compliant.

What is in this house that demands so much electric? Most properties will happily run on a 60 or 80 amp fuse without incident.

PS - is this 1ph or 3ph?
 
Well spotted, I didn't really look at that bit!
LOL - yeah it jumped out because (without checking) I believe its rated at 104amps surface mount meaning 40m and possibly buried might de-rate this by 40% but I will let someone else check up the figures, I'm winging the response without the tables here ?
 
You're stuck between a rock and a hard place with this. From a purely electrical perspective the DNO fuse provides the overload protection, however there is the fabled 3m rule which says you need to provide a CPD and some discrimination. Your quick option would be an 80A KMF, there isn't really anything between that and 100A. If you want to get as close to 100A as possible just not quite (and I'd be intrigued on a domestic, but that's another story...) then you need to look at electronic adjustable MCCB's and then you're into big money.

Off the cuff I can tell you the cable is well undersized for your needs.

You need to establish the installation method, we already have the length and cable type so you then need to apply cable calc's to establish the recommended cable size for this run to ensure your VD is compliant.

What is in this house that demands so much electric? Most properties will happily run on a 60 or 80 amp fuse without incident.

PS - is this 1ph or 3ph?
Ok, so its buried underground, on the cable calculator I used, I admit I have forgotten all the manual calcs, 25mm came out as more than sufficient for 100a with a 2.7% VD... if buried! I am happy to be schooled on this because its been some time since school and I have never come across a situation like this.

I should add that this is a kind of temporary measure as a second house is being built on the land and the service head will be moved to the main house and a second supply put in to feed to the first house. Then we will be able to adhere to the 3m rule. ( which i thought had dropped to 1m now)

The house could survive on 80 Amps however they may want to put a kiln in it at some point. hence the higher requirement.
 
433.3.1 (iii) does actually give you an answer to this, if you can get the DNO to agree it
 
Just to add here, temp' supplies still have to comply to the same regulations as permanent installs, the ability of the cable to carry the load and meet requirements of VD does not change because you are only using it for several weeks/months.

Can we also ask why such a huge demand for a house, is it a large state house?
 
Just to add here, temp' supplies still have to comply to the same regulations as permanent installs, the ability of the cable to carry the load and meet requirements of VD does not change because you are only using it for several weeks/months.

Can we also ask why such a huge demand for a house, is it a large state house?
oh I completely agree, but this seems to be on the edge of 25mm and 35mm cable from what earlier posts have said. As i mentioned it may have a kiln in it which has a large draw, but if they arent using it at the same time as the induction hob, oven, washing machine then im sure it will be fine at 80.
 
ok so its coming at 2.2% for 78amps across 40m is this not close enough to the rule of thumb? Also I wasnt aware that it was 2% for submains, can you reference that please?
It's not referenced but the volt drop is from the source of supply to the end of your final circuits. If you use 2.2% on your distribution circuit that gives you only 0.8% to play with for lighting.

What is the expected maximum demand for the new build?
 

Reply to Overload Protection of "submain" in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
510
hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
326

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top