Hi folks, not posted in a while but I have been having a few interesting discussions about this one !!!
I have come across a cooker connection outlet which is wired in 6mm and supplied via 45a dp sw and a 32a MCB
Now in this outlet I have an oven at 3kw wired in 2.5mm HOFR and a sparker for the hob wired in 1mm flex.
Guy from work reckons this is a C1 as the 2 cables are not rated to 32 amps. I disagree with him, While I think it is bad practice and would probably fit dual box with 2 s skts or spurs.
My take on it though is it could probably be coded c3 due to the fact that the oven and sparker will not draw anymore load than what they are rated at and the cables supplying them are adequate for that load hence overload protection may be omitted. As long as my circuit complies with fault protection requirements, it is not best practice and I would improve but would it warrant a C2 or C1!! And an unsatisfactory EICR ?? In my opinion no. But I have heard a few different opinions on this one !!!
What you describe is NOT a C1 - a C1 is danger NOW.... i.e live components that can be touched.
Could be a C2 BUT you can reduce the CSA of a cable and as long as the cable is less than 2 meters - so no code.
If I did the EICR, I would probably comment on the set up to CMA
Does the ignition circuit cable incorporate a cpc. Have you considered short circuit protection between line/neutral, I would personally C2 this.
There is a CPC in the sparker cable yeah, with regards to l/n short circuit is that going to be an issue over 2m of cable ? I am no an engineer so not sure, but is the situation any different from a 2.5mm spurred of a ring on a 32a MCB ? This could easily be more than 2m long ?
You need to consider the magnitude of fault current on the 1.0 cpc regardless of cable length. Conductor csa should be selected so it can withstand fault current with no adverse effects.
What is this 2 meter rule?
I'm aware of fault protection and overload protection being placed on the load side at a maximum Of 3 meters when there is a reduced ccc or reduction in CSA and 2 other considerations required but not sure on this 2 meters?
Would be time to do everyone's favourite adiabatic equation to see if the thermal constraints of the 1.0mm are adequate for a32amp mcb.
Or if the let through energy is Less than the formula K2S2 => I2t
Bit of a chew on really
Had a quick look in the BYB. The '3m rule' is to do with reg 433.2.2.
Something for me to read in a bit more detail and compare against fault protection requirements sometime.
Reply to Overload protection omission in the Commercial Electrical Advice area at ElectriciansForums.net
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
4K