Hi Guys I hve a ring main that keeps tripping, but it also trips the main rcd on the board, is there a possibility that it is being overloaded? There are about 6 computers a franking machine a photocopier coffee machine and a few other gadgets on this one ring of 10 sockets! Should the ring be split down to maybe 2 or 3 seperate rings??? Take into account this is on a second dist board in a house that has had a conversion for a small office. There were only 3 lights and 10 sockets added on.
Items with switch mode power supplies such as laptops, PC's, printers etc can have standing leakage up to 3mA per device and this wouldn't be considered a fault current. From the load you describe there could be standing leakage in excess of 20mA which doesn't leave much before the 30mA tripping threshold is reached. Maybe clamp the live and neutral together in an earth leakage clamp meter and measure the normal standing leakage with all appliances switched on. You may need to install RCBO's on each circuit rather than a single main RCD.
Reply to overload in the UK Electrical Forum area at ElectriciansForums.net
When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...