overload | Page 2 | on ElectriciansForums

Discuss overload in the UK Electrical Forum area at ElectriciansForums.net

N

Norn Iron

Hi Guys I hve a ring main that keeps tripping, but it also trips the main rcd on the board, is there a possibility that it is being overloaded? There are about 6 computers a franking machine a photocopier coffee machine and a few other gadgets on this one ring of 10 sockets! Should the ring be split down to maybe 2 or 3 seperate rings??? Take into account this is on a second dist board in a house that has had a conversion for a small office. There were only 3 lights and 10 sockets added on.
 
Items with switch mode power supplies such as laptops, PC's, printers etc can have standing leakage up to 3mA per device and this wouldn't be considered a fault current. From the load you describe there could be standing leakage in excess of 20mA which doesn't leave much before the 30mA tripping threshold is reached. Maybe clamp the live and neutral together in an earth leakage clamp meter and measure the normal standing leakage with all appliances switched on. You may need to install RCBO's on each circuit rather than a single main RCD.
With using rcbos for each circuit does this mean then that each circuit will have 30mA as opposed to every circuit having 30mA off the main RCD?
 

Reply to overload in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Replies
2
Views
442
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top