Right following on from my last post.
i rewired a pizza oven circuit as the oven was being moved.its done in 16mm twin and earth.protected by a 50 a mcb.
guynfoned tonight saying after half an hour the circuit tripped so went up the oven is 13 kw can this be an overload?should I put a 63a mcb in.
circuit always resets when mcb is put back so don't think it's a fault
many thanks
Neva re-wire an oven when it's being moved or you'll have to start PAT testing it mate...............wait until it's stopped:)
56.5A. could just trip the 50A after a while. esp if it's in a kitchen, high ambient temp. stick a 63A in, cable installation method allowing for such uprating.
Cool thanks telectrix he was only doing staff training tonight and both fans I am installing aren't up yet they are coming tomorrow so he says the place was boiling once they had started.
16mm, clipped direct will handle 87A, so you've got some latitude with your MCB.
It's clipped in loft then in 50 x 50 trunking
This vital bit of info is a game changer ..... as its run through a loft unless measures have been taken to ensure existing or future insulation of the loft will not de-rate the ccc of the cable unless its been already implemented in design... then your running in trunking.... i see issues already in uprating mcb!..... although its an existing install you are making alterations to it and must ensure the circuit is fit for purpose..... 2yrs down the line someone lags the loft and 1week later Pizza shop burns down!!!!
Ironic that if it already runs through the insulation more than 100mm then the 50amp mcb is too big a set-up you hopefully have calculated if need be, if no insulation present you should ensure that installation of it will not effect cable... i use a warning notices to warn of fire hazards if insulation is fitted over cables in a loft and have my company details along with it.
Check out post 10 WHOopps! Think OP may have some problems here after 2 threads he chucks in spanner!:eek:mg_smile:
Tbh honest I doubt consideration has been given previously to the installation method, as he can't even work out if 13kw is too much for a 50a breaker, a pretty basic sum
Reply to Overload? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...