I will also add here, regardless whether a torque tool or just judgement has been used, copper - especially stranded can suffer from creep, this is when you have tightened the terminal and over the next few hours or so the copper will naturally creep into any tiny gaps as it is under high pressure, this can lead to a tight terminal become loose on its own but terminal hole design and grub screw play a key role in eliminating this, this is why meter terminals are often circular and the grub is wider than the bore.
 
That is really scary, you guys are trained to fir electrical meters, the device that has the highest current passing through it and have not been given instruction on how tight the terminals should be? the detail should be in the Mi for the meter in question. and I would have thought that a preset torque driver used to tighten the terminals.
Oh I totally agree, especially considering one mans tight is another mans loose or one mans loose is over tight.
 
No torque tools then bunch of idiots, that would be my first option, know wonder there are fires etc.
We only do what we are told/trained to do. I’m not disagreeing I think the training isn’t good enough. You are given 12 weeks training. 16 meter installs as experience then set off on your own. And don’t get me started on gas
 
Yes of course.
More details would be nice, don't want to pry, but was that an in house course run by the company you work for? if you are unsure of any aspects of your role then I would have expected some sort of employee advice centre you could call on, to be honest with you I do find it odd, regarding the sort of work you are employed to do, and yet not much information or engineering equipment provided, please don't think I'm being dismissive of your role, just seems an odd question seeing as you have had training etc, anyway ask for information on torque setting and tooling for the equipment you are installing, good luck.
 
No we do not get given torque screwdrivers for wiring meters. It’s done on feel alone. Hence why I tighten until I can’t tighten anymore. Just worried that could be damaging the copper strands.
Well then that is bad, don't know your experience in the electrical field, so where does you experience of "feel" comes from, I'm not practicing this trade any more as I'm retired but, it is odd that they expect this from you seeing as it is at the start of an electrical installation, what with the loads that will be expected.
 

Reply to Overtightening Meter Terminals in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
859

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top