http://www.microgenerationcertification.org/images/PV Book ELECTRONIC.pdf

There are guidelines rather than rules - the important thing is to be able to prove your design will take the loads imposed by wind.

Anything less than 500mm puts you in the edge zones which requires more careful design.

In general you can be 300mm away from the roof edge without the design becoming ridiculous - this is dependent upon the roof and the situation. A hipped roof will experience more turbulence, and one next to the sea will require extra care...etc.

How tall is the building? A single storey garage in a sheltered location will be more tolerant than a 4 storey house by the sea.

2 other factors to consider are:

1) Lifting tiles to fit hooks can damage mortared ridges and verges. A rule of thumb is 300 at all edges for plain tiles, 300 at the gutter and 500 from edges and ridge for concrete Redland 49 type and large format modern interlock will possibly require 600 from the ridge. Not a problem for dry ridge and verge construction and slate roofs of course.

2) going too close to the gutter with a bolt-on system can lead to water overshooting the gutter and causing damp issues. 300mm min on a 45deg roof is a good rule of thumb.
 
I should clarify regarding the lifting of tiles that the margins I suggest are for the edges of the panels to the margins of the roof. Assuming you are using panel base rails, your hooks can be upto 500mm from the edges of the panels (so 1m away from the roof edge for a concrete interlocking roof) with no chance of damaging the verge cloaking detail.

Bear in mind that if you are going into the roof edge zones you really want to keep the panel / hook overhangs to less than 300mm ideally. It depends on the rail / hooks you are using, the rafters details and expected windloads.

Another thing, when I worked at SC (back at the start of the century) we did some testing at BRE which suggested that with some rail / panel combinations oscillation could occur which would gradually loosen mortared ridge tiles.

Another reason to keep panel overhangs as short as possible...
 

Reply to Panel Positions in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
499
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
973
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

I'm looking for advise on the type of mounting system suitable for these types of tiles. These are sort found on new build houses. They are...
Replies
0
Views
342
You need to pass the job on to someone who is competent and up to speed with solar installs and regulations .
Replies
4
Views
747

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top