Hi guys,
I've spent the last few weeks reading through the site and have got to say I'm very impressed with the patience and knowledge you all have.
This topic has been discussed and i'm sorry for bringing it up again but I would still like your opinion on the way I test and record my Zs readings.
I'm in an Industrial environment and old school ( sparky for 38 year).
I'm the only spark on site and run my own maintenance and test scheme and unlike you guys don't get inspected by governing bodies etc.
So here lies my problem.
The factory where I work has 3 sets of metal housed overhead busbars fed with 70mm SWA cable.
These have fused tap off boxes which then drop down and feed wall Isolators which then feed D/Boards which then feed Machine Isolators which then feed machine transformers which then feed fixed machines.
All of these are metalclad and fed with Swa cable.
edit....I also always include a seperate earth in the feed cables and the supply is TNS 3p+N.
Now being 'old school' you can imagine I have bonded everything in site and then bonded wall isolators D/B's and busbars to the factory girders.
My transformer is on site and approx 20 metres away so you can imagine my Zs readings are absolutely perfect and well below the allowed figures............problem is this includes all parallel earth paths as it would be impossible for me to disconnect them all.
On my forms I record all the Zs readings from all the various points and put a side note saying these results include parallel earth paths.
I'm happy in my own mind that these extra parallel paths are permanent and will not be removed so treat them as part of the earthing system and therefore my Zs readings are acceptable albeit much lower than would be the case without the extra paths.
Am I right in this assumption or should I be doing something different?
I look forward to any input you may have it will be greatly appreciated.
Allan
I've spent the last few weeks reading through the site and have got to say I'm very impressed with the patience and knowledge you all have.
This topic has been discussed and i'm sorry for bringing it up again but I would still like your opinion on the way I test and record my Zs readings.
I'm in an Industrial environment and old school ( sparky for 38 year).
I'm the only spark on site and run my own maintenance and test scheme and unlike you guys don't get inspected by governing bodies etc.
So here lies my problem.
The factory where I work has 3 sets of metal housed overhead busbars fed with 70mm SWA cable.
These have fused tap off boxes which then drop down and feed wall Isolators which then feed D/Boards which then feed Machine Isolators which then feed machine transformers which then feed fixed machines.
All of these are metalclad and fed with Swa cable.
edit....I also always include a seperate earth in the feed cables and the supply is TNS 3p+N.
Now being 'old school' you can imagine I have bonded everything in site and then bonded wall isolators D/B's and busbars to the factory girders.
My transformer is on site and approx 20 metres away so you can imagine my Zs readings are absolutely perfect and well below the allowed figures............problem is this includes all parallel earth paths as it would be impossible for me to disconnect them all.
On my forms I record all the Zs readings from all the various points and put a side note saying these results include parallel earth paths.
I'm happy in my own mind that these extra parallel paths are permanent and will not be removed so treat them as part of the earthing system and therefore my Zs readings are acceptable albeit much lower than would be the case without the extra paths.
Am I right in this assumption or should I be doing something different?
I look forward to any input you may have it will be greatly appreciated.
Allan