Hi there

Doing some testing at moment. R1 + R2 readings coming in lower than R1 + Rn. Cpc neutral and live all disconnected. There is alot of containment on job and adaptable boxes are all fly leaded to earth. My thoughts are they are parallel earth paths but guy working with seems to think because cpc disconnected at board it can' be. Who is right basically? Thanks
 
Hi Pete I don' think I can do end to end readings as over multiple floors? The leads were nulled yes. Have just tested a seperate circuit and how similar readings with a 0.30 lower difference again with r1 + r2 this does parallel paths no?
End to end readings are for RFCs, this is where the confusion comes from, if you had mentioned that it was a lighting circuit the confusion would have come to the for earlier, you may need to brush up on your testing procedures Mate, the question begs, how did you get your R2+R2 results?
 
Hi Pete I don' think I can do end to end readings as over multiple floors? The leads were nulled yes. Have just tested a seperate circuit and how similar readings with a 0.30 lower difference again with r1 + r2 this does parallel paths no?
End to end readings are for RFCs, this is where the confusion comes from, if you had mentioned that it was a lighting circuit the confusion would have come to the for earlier, you may need to brush up on your testing procedures Mate, the question begs, how did you get your R2+R2 results? Message to oneself don't assume anything or that anyone knows what they are doing.
 
Now we know it is a radial then yes any metal containment will affect readings due to parallel paths unless you isolate the cpc from the containment. Disconnecting the cpc at the board will have little effect unless the cpc goes to a single point of utilization.
 
Now we know it is a radial then yes any metal containment will affect readings due to parallel paths unless you isolate the cpc from the containment. Disconnecting the cpc at the board will have little effect unless the cpc goes to a single point of utilization.
Deleted
 
Hi there

Doing some testing at moment. R1 + R2 readings coming in lower than R1 + Rn. Cpc neutral and live all disconnected. There is alot of containment on job and adaptable boxes are all fly leaded to earth. My thoughts are they are parallel earth paths but guy working with seems to think because cpc disconnected at board it can' be. Who is right basically? Thanks
There could be parallel paths if the conduits are straight into the board or into trunking and the trunking is bonded and the building structure can also create a parallel path to earth
 
End to end readings are for RFCs, this is where the confusion comes from, if you had mentioned that it was a lighting circuit the confusion would have come to the for earlier, you may need to brush up on your testing procedures Mate, the question begs, how did you get your R2+R2 results? Message to oneself don't assume anything or that anyone knows what they are doing.
 

Reply to Parallel paths on R1 + R2 test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top