Yes probably overkill E54 but it would do the job and on a large scale upgrade of existing could actually be the most cost effective method but as i said i was just throwing it out there that it isn't against reg's if calculated correctly - but agree beyond your average Electrician out there so yes following the rule of thumb always same csa, length and route.
 
Yes probably overkill E54 but it would do the job and on a large scale upgrade of existing could actually be the most cost effective method but as i said i was just throwing it out there that it isn't against reg's if calculated correctly - but agree beyond your average Electrician out there so yes following the rule of thumb always same csa, length and route.

Why would anyone, least of all a Design Engineer leave a parallel circuit in place with differing CSA on a large scale upgrade, that would be defeating the whole point of the upgrade.

I know what you're saying, but as i said earlier there are always way's to get over an existing problem, but 9 X out of 10 the additional costs and hassle just aren't worth not doing the job properly... lol!!
If the reg's condone such an installation, i haven't come across it. I'll have to have a look later today, if i have time.
 
Why would anyone, least of all a Design Engineer leave a parallel circuit in place with differing CSA on a large scale upgrade, that would be defeating the whole point of the upgrade.

I know what you're saying, but as i said earlier there are always way's to get over an existing problem, but 9 X out of 10 the additional costs and hassle just aren't worth not doing the job properly... lol!!
If the reg's condone such an installation, i haven't come across it. I'll have to have a look later today, if i have time.

I agree and see why your reaction to my original comment now, im jumping between forums and was on auto pilot the variable sized cores comment was relative to single cores in parallel across phases; if i remember rightly you are required to maintain equal csa on the same phase but can in certain set-ups have other phases of different csa (although not as a standard install of a 3ph supply with linked O/L protection across the phases). I didn't mean variable sizes between the same phase.... relative to 2 or more multicore cables in parallel then this doesn't apply to that senerio as yes equal csa required deffo....

It was merely an extreme example to back up my suggestion that parallel systems do function correctly and safely with unequal load sharing if designed carefully and protected properly.

This i got carried away here and went on a non-constructive tangent but ill see if i can reference what i mean another time as its time for the pit. :)
 
Last edited by a moderator:
Can we stop the squabbling.

Equal parallel feeds = Good
Unequal parallel feeds = Not good, but with proviso’s acceptable.

I ran a 240mm² PVCSWA to bolster two 0.3 PILCSWA’s. Not ideal but it got our arse out of the fire. The PILCSWA terminations had been done with wax (only time I’ve ever seen this). They were so hot they were spitting wax out of the termination.

Needs must at times!

The switchgear catching fire is another story :smilielol5:
 
Can we stop the squabbling.


quabbling.

Equal parallel feeds = Good
Unequal parallel feeds = Not good, but with proviso’s acceptable.

I ran a 240mm² PVCSWA to bolster two 0.3 PILCSWA’s. Not ideal but it got our arse out of the fire. The PILCSWA terminations had been done with wax (only time I’ve ever seen this). They were so hot they were spitting wax out of the termination.

Needs must at times!

The switchgear catching fire is another story :smilielol5:

Are we squabbling?? I didn't think that we were...

Are you saying this set up was actually left in place as part of the factory installation??
 
Are we squabbling?? I didn't think that we were...

Are you saying this set up was actually left in place as part of the factory installation??

For many years. I said it wasn’t ideal but it got things cooled down a bit.

0.3”² = roughly 210mm². I had ½ a day to get the new cable in along with a new GEC 1200A ACB and two GEC 1600A bus section switches in to a SWS switchboard.

Must be nice to work with all new equipment that never gets over stressed. Over time things get up rated and you don’t get to know until things start cooking. One compressor on this MCC was uprated from 300HP to 450HP a couple of pumps 60HP to 120HP. We were getting a quart out of the original pint post.

As a said it must be great I do new installs only.
 
For many years. I said it wasn’t ideal but it got things cooled down a bit.

0.3”² = roughly 210mm². I had ½ a day to get the new cable in along with a new GEC 1200A ACB and two GEC 1600A bus section switches in to a SWS switchboard.

Must be nice to work with all new equipment that never gets over stressed. Over time things get up rated and you don’t get to know until things start cooking. One compressor on this MCC was uprated from 300HP to 450HP a couple of pumps 60HP to 120HP. We were getting a quart out of the original pint post.

As a said it must be great I do new installs only.


Believe me, new installs can just as easily go pear shaped too!!
 
I’ve got to admit I’ve enjoyed keeping things going and doing it on the cheap.

As for new stuff going wrong, a brand new Brush switch board was delivered. I refused point blank to have anything to do with it. ⅔ of it was scrapped before a single cable was connected, replaced by GEC gear. All the bus-bars replaced in the bits we did keep. It was a cock up on a monumental scale.
That was over 25 years ago, I still have a giggle about it.
 
The two differing impedance of the cables will sort out the current sharing, its protecting the the cables against fault where the problem lies.

This is the case for smaller cables but once you go large you have a lot more than measured impedance to consider as the reactive component of the impedance becomes a major player and positioning/arrangment and distance apart all become crucial to the effects of load sharing and need to be implemented in design to the best we are able.
 
This is the case for smaller cables but once you go large you have a lot more than measured impedance to consider as the reactive component of the impedance becomes a major player and positioning/arrangment and distance apart all become crucial to the effects of load sharing and need to be implemented in design to the best we are able.

Measured Impedance?

Impedance Triangle R,Z and X ;)
 

Reply to Parallel Supplies in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
800
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
983

Similar threads

Controllers that are intended to control twin immersion cylinders only allow one to be powered at a time.
Replies
5
Views
429
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top