twin / parallel feeds are pretty common on submains larger than 300mm.

struggling to think of anything else to add to be honest lol.

er , carry on.

;-)
 
hoo hoo Can I join in this thread?? I'll invite Eng54 as well... :)
 
Parallel circuit/supply needs all conductors to be of the same CSA, follow the same route, cables be of the same type and construction. Parallel circuits can consist of several conductors/cables not just two. Such circuits can and do offer many advantages over a single much larger conductor/cable installation....

If designing the OP's circuit from scratch probably 2 X 16mm would be selected, but in some circumstances even 2 x 10mm could replace a single 35mm cable....
 
so, in a nutcase, sorry, nutshell, as OP already has a single 25mm, the solution is to parallel a second 25mm cable in.
 
i already said it in post #6.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Parallel Supplies
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
58

Advert

Thread statistics

Created
Guest 004,
Last reply from
Chr!s,
Replies
58
Views
8,608

Advert

Back
Top