Joined
Aug 21, 2014
Messages
122
Reaction score
20
Location
Wales
One of the questions on a recent Part P assessment was how would I wire an external outbuilding if the earthing arrangement to the property was PME.

I said I would run a three core SWA from the property to the outbuilding and use the cable armour and the third core as the exported CPC.

I was highly criticised and was told that I should install a rod at the property and at the outbuilding.

I can find no mention of this in 17th ed AMD3 book, can anyone tell me where i would find this if it is the case.

I have had a couple of other Assessments previously where they have checked out building installs and never mentioned this so I am not happy.
 
the assessor is wrong. you would normally only need to make the outbuilding TT if it was a metal structure or if the 3rd core of your SWA was inadequate for bonding purposes (min. 10mm for PME ).
 
I've been hearing through the grapevine that Stroma are starting to become extremely harsh with their assessments. On the face of it this should worry us less than the other extreme, but some of the reasons for non conformances do make you wonder whether they do it to make you pay for a re-visit.

I've heard this through my Elecsa assessor recently (so he ma ybe biased), but also through a friend who is registered through Stroma. He received a non conformance due to fixing sockets inside kitchen cabinets. The assessor claimed accessories had to be fixed to the fabric of the building and not kitchen furniture. Complete garbage as we all know. I forget whether he had to have a re-visit or not.
 
If the outbuilding had extraneous conductive parts then I would have put a rod in.

The question had no relevance to the job he was assessing this time as it had a TT earthing arrangement and no specific details were given in the question, just how would I do it with PME Earthing
 
If the outbuilding had extraneous conductive parts then I would have put a rod in.

The question had no relevance to the job he was assessing this time as it had a TT earthing arrangement and no specific details were given in the question, just how would I do it with PME Earthing
 
makes you wonder sometimes if some of these assessors are not as knowledgeable as they should be. maybe he's a short course ex traffic warden and hasn't got out of the habit of parking penalty ticket targets.
 
Was it a fairly large bloke, pasty complexion, who ate sausages for lunch ?? If so then it might be the same o who assessed me; told me that my SWA to an outbuilding needed to be RCD'd ?? and marked it as a non-conformity. I complained and had it over-ruled. I think his name was Andy (might be wrong thou as it was 2 years ago). What his name ? If its the same bloke we can get him fired; seriously
 
Was it a fairly large bloke, pasty complexion, who ate sausages for lunch ?? If so then it might be the same o who assessed me; told me that my SWA to an outbuilding needed to be RCD'd ?? and marked it as a non-conformity. I complained and had it over-ruled. I think his name was Andy (might be wrong thou as it was 2 years ago). What his name ? If its the same bloke we can get him fired; seriously

Easy tiger.

I think this is a case of old money versus new money. I mean darling, you get wot you pay for these years. Stroma are clearly new money, and trying to make themselves look respectable, against the lords from Certsure. I mean who pays pennies to be in a decent club. Standards are clearly slipping. Wasn't like this a few years ago, ya paid ya wod, and got serviced :D
 
They phoned me a few weeks ago asking me to leave NICEIC and join Stroma. Didn't take them up on the offer. For simple fact it would mean changing all my stationary and business cards that have the NICEIC logo on:tearsofjoy::laughing: Told them it would cost almost as much as I would save joining to change it all and buy new advertising stuff and T-shirts etc...
I do find no matter what scheme you are with you get good assessors and bad. I had heard that Stroma were on a recruiting drive for some field assessors as they had a shortage and there low fees had left them playing catch up.. might explain why they are doing bi-annual assessments and even phone renewals now in the years in between!? Maybe they are being a bit lax on the recruitment of assessors?
 

Reply to Part P assessment question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
Replies
21
Views
987
nicebutdim
N
IMO the NICEIC and NAPIT are two quangos that have made a laughing stock of the UK's electrical industry aided and abetted by the Labour...
Replies
10
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
834
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
823
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks